Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PQM HTML Webpage Comtrade file time stamp

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PQM HTML Webpage Comtrade file time stamp
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Paul_Crouch
Paul_Crouch
Explorer

Posted: ‎2025-12-11 01:03 PM

0 Likes
2
472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-11 01:03 PM

PQM HTML Webpage Comtrade file time stamp

When I view the Comtrade waveform on the HTML page, the time stamp is UTC time.  If I were to view the same waveform file in ION setup it has the proper time stamp for the region and time the meter is set for. 

This is specifically for PM8240 and ION 9K products, but could be for others.

 

Is there some setting I am missing to ensure the HTML page Comtrade waveform view are showing proper time stamps. 

It is more a nuisance than a problem, but if looking at multiple meters at the same site then the additional check for time can make trouble shooting take longer. 

 

I can provide screenshots if needed.

Labels
  • Labels:
  • ION9000
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-12-12 08:11 AM

0 Likes
0
461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-12 08:11 AM

Hello @Paul_Crouch 

The meter will store all timestamps as UTC, waveforms, data recorder logged data, event logs etc. Different user interfaces will convert the UTC time to local time. Web pages, ION Setup, PME etc. each have different decisions to show either local time or UTC time.

 

The phrase "proper" can be a bit subjective. Inside the COMTRADE file itself, the timestamp is UTC. Could also be confusing to people to read the contents of the COMTRADE file and see a difference between what is on the web page and what is in the file.

 

The meter's webpages use JavaScript to display the timestamps on the web pages. If you know JavaScript you could in theory apply the time difference between local and UTC inside the JavaScript. I do not have an example I could provide. Note that every firmware upgrade would overwrite any changes you made.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-12-12 08:11 AM

0 Likes
0
462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-12 08:11 AM

Hello @Paul_Crouch 

The meter will store all timestamps as UTC, waveforms, data recorder logged data, event logs etc. Different user interfaces will convert the UTC time to local time. Web pages, ION Setup, PME etc. each have different decisions to show either local time or UTC time.

 

The phrase "proper" can be a bit subjective. Inside the COMTRADE file itself, the timestamp is UTC. Could also be confusing to people to read the contents of the COMTRADE file and see a difference between what is on the web page and what is in the file.

 

The meter's webpages use JavaScript to display the timestamps on the web pages. If you know JavaScript you could in theory apply the time difference between local and UTC inside the JavaScript. I do not have an example I could provide. Note that every firmware upgrade would overwrite any changes you made.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Paul_Crouch
Paul_Crouch
Explorer

Posted: ‎2025-12-12 12:28 PM

0 Likes
0
377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-12 12:28 PM

After I submitted this yesterday, I did read other tickets.  Applying Java Script is not a good solution, not when one of my Date Canters could have more than 25 meters at a site.  The other solution is to have enough users request a change from sales team to provide an internal SE based solution for all meters.  I understand this a merely a nuisance, but if there is utility network input issue which small amount of time needed to true up time stamps for a true time start can take a lot of time that would be better spent actually troubleshooting or evaluating an issue.  This seems to with Java script, SE is putting the onus on the user(s) to have some kind of solution.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore