ION Meter Setpoint Module – Setup Register Read/Write via Modbus

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION Meter Setpoint Module – Setup Register Read/Write via Modbus
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
527
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
139
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2025-12-09 07:52 AM

0 Likes
6
139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-09 07:52 AM

ION Meter Setpoint Module – Setup Register Read/Write via Modbus

Hi All,

 

I’m using the setpoint module on an ION meter to configure some alarms. I’m wondering if the setpoint high/low limits are available for read and write via Modbus?

 

Stuart_Cheng_0-1765295421754.png

 

 

I tried setting up a Modbus tag, but it seems I can only select the output registers and not the setup registers. Has anyone encountered this or know a workaround? Thank you!

Labels
  • Labels:
  • ION Setup
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
Admiral

Posted: ‎2025-12-09 10:55 AM . Last Modified: ‎2025-12-09 10:59 AM

0 Likes
0
128
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-09 10:55 AM

Hi @Stuart_Cheng 

 

Given that using the Modbus Slave Module makes ION register values available to a Modbus master device, or that additional Modbus registers such as Numeric Registers starting at 56001–59999, are assigned for writing values to some ION module registers over Modbus:

Mehran_Mehrnia_2-1765304449767.png


it’s important to note that, as mentioned in another forum discussion on 'Writing to Modbus Registers' the setup register values of a module cannot be written over Modbus and cannot be linked to the Modbus Slave Module for reading or to an External Numeric module for writing.

 

Please also note that, the meter's Security Options Module (SOP1) has its Modbus Map Access setting changed from the default of "No" to "Yes" to permit Modbus writes to your custom registers.


Using native ION application software such ION Setup, PME apps, it's possible to read/write the Setup registers of ION Modules.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-12-09 10:39 PM

0 Likes
0
111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-09 10:39 PM

Hello @Stuart_Cheng ,

 

I tried to link a setpoint module's Setup registers directly to a modbus slave input was unable to make the link. However I was able to link to an Arithmetic module. You could feed the output of the Arithmetic module to a modbus slave module to get access to the value via Modbus.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 6
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
Admiral

Posted: ‎2025-12-09 10:55 AM . Last Modified: ‎2025-12-09 10:59 AM

0 Likes
0
129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-09 10:55 AM

Hi @Stuart_Cheng 

 

Given that using the Modbus Slave Module makes ION register values available to a Modbus master device, or that additional Modbus registers such as Numeric Registers starting at 56001–59999, are assigned for writing values to some ION module registers over Modbus:

Mehran_Mehrnia_2-1765304449767.png


it’s important to note that, as mentioned in another forum discussion on 'Writing to Modbus Registers' the setup register values of a module cannot be written over Modbus and cannot be linked to the Modbus Slave Module for reading or to an External Numeric module for writing.

 

Please also note that, the meter's Security Options Module (SOP1) has its Modbus Map Access setting changed from the default of "No" to "Yes" to permit Modbus writes to your custom registers.


Using native ION application software such ION Setup, PME apps, it's possible to read/write the Setup registers of ION Modules.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-12-09 11:40 AM

0 Likes
1
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-09 11:40 AM

Hello @Stuart_Cheng ,

 

To link a setup register in ION Setup, before you click the link button hold down the Ctrl key then click the link button. This will tell ION Setup to use Setup registers rather than output registers. You can use this to link Setpoint module setup register to Modbus Slave module input to be able to read the High/Low limits. 

 

Writing to a setup register is a different story. Registers linked to Modbus slave modules cannot be written to. Only if the setup register is linking to the default Modbus mapping can a write be possible.

 

External numeric modules can be written to via modbus if permissions are set. You could change the framework to do calculations based on External numeric value and the measurement in question. Then link the output of the calculation to the setpoint module to make the alarm. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-12-09 10:39 PM

0 Likes
0
112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-09 10:39 PM

Hello @Stuart_Cheng ,

 

I tried to link a setpoint module's Setup registers directly to a modbus slave input was unable to make the link. However I was able to link to an Arithmetic module. You could feed the output of the Arithmetic module to a modbus slave module to get access to the value via Modbus.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities
Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2025-12-12 12:57 AM

0 Likes
1
66
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-12 12:57 AM

Hi @Charles_Murison @Mehran_Mehrnia,

 

Thanks for sharing all the information. I also ran some tests and would like to confirm a few points:

 

  1. Regardless of the ION module used, setup registers cannot be linked to a Modbus slave module for reading.

  2. When writing values to the ION meter via Modbus, the available registers are limited to those listed in the Modbus Map file—specifically ranges 52001–53000, 54001–56000, and 56001–59999. These registers are predefined and cannot be modified.

    Stuart_Cheng_0-1765529659769.png

     

  3. To read or write the limit of a setpoint alarm, an alternative approach is to write the limit value to an external module, link it to an Arithmetic module for logic or calculations, and then use Setpoint module to generate alarm.

    Appreciate any feedback!
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-12-12 07:46 AM

0 Likes
0
54
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-12 07:46 AM

Hello @Stuart_Cheng 

1. That is my understanding however I have not tested with every possible module. At least with ION Setup.

 

2. Refer to the detailed modbus map section, look for registers with R/W.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2025-12-14 05:34 PM

0 Likes
0
5
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-14 05:34 PM

Thank you @Charles_Murison!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore