Regarding Com'X 510

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

sesa198688_brid
Lieutenant Lieutenant
Lieutenant
0 Likes
4
329

Regarding Com'X 510

1.jpg

  1. Based on this Architecture, Can Com'X 510 log the data from Link 150 downstream power meters (Daisy chain)?
  2. If it is Yes means, how many meters’ data can be log inside Com'X 510?

Thanks & Regards,

Mala

4 Replies 4
SudhaSneha_D
Commander Commander
Commander
0 Likes
2
280

Re: Regarding Com'X 510

Hello Mala,

Yes you can set up the ComX 510 to log data from the devices downstream of the Link 150.

ComX_Link150.png

The ComX connects to the Link150 as any other ModbusTCP device. Once connected you can discover the downstream devices.

-Sneha

DK-Michael
Commander Commander
Commander
0 Likes
0
280

Re: Regarding Com'X 510

You can connect up to 64 devices in total. I have no idea if there exist a calculator that tells you for how long you can store data. I guess that depends on the log interval and amount of devices.

________________________________
Michael Johansen
Solution Architect
M +4528991535
E michael.johansen@se.com
LinkedIn https://www.linkedin.com/in/mich4el/
sesa198688_brid
Lieutenant Lieutenant
Lieutenant
0 Likes
1
280

Re: Regarding Com'X 510

Thanks

sesa198688_brid
Lieutenant Lieutenant
Lieutenant
0 Likes
0
280

Re: Regarding Com'X 510

Thank you