Hey Everyone,
We have a very large customer who have number of our meters (ION 7700, ION 7350, ION 7650) and have questions that I could not answers. I am hoping this forum can help.
From the customer:
1. Ideas on password management (we have 1000s of meters and we need enterprise level solution)
2. On 7350 we found that we can change PT and CT ratios without password from the ION enterprise webpage. Is this correct?
3. When is the EOL on 7650 meter and what would be a direct replacement for the 7650
4. Is there a retrofit kit for replacing ION7700 to replace with like metes without major effort.
5. What is the maximum number of concurrent SCADA connections for PM8244 and 7650 for communication over ION, DNP3, and Modbus protocol.
Thanks in advance.
Harvey. @markkozlowski
Link copied. Please paste this link to share this article on your social media post.
Hi Harvey,
I can answer some of these questions:
3. When is the EOL on 7650 meter and what would be a direct replacement for the 7650
We don't have the answer to this question yet. I will send you an email with our current plan.
5. What is the maximum number of concurrent SCADA connections for PM8244 and 7650 for communication over ION, DNP3, and Modbus protocol.
Please see attached image. This info is on page 44 of PM8000 user guide
Link copied. Please paste this link to share this article on your social media post.
4. Is there a retrofit kit for replacing ION7700 to replace with like metes without major effort.
The least effort is ION7650 TRAN version. If you do not need the transient capture you may use PM8000 without display.