Question regarding PCS+ error

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Question regarding PCS+ error
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
2WON
2WON
Cadet

Posted: ‎2024-09-25 06:42 PM

0 Likes
4
551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-25 06:42 PM

Question regarding PCS+ error

 

KakaoTalk_20240911_090100171_04.jpg

As shown in the photo, there is a harmonic filter error. Could this issue be because the IT/BP switch is not in the open position? The system is a 3-phase, 3-wire, 440V delta ungrounded IT system.

The CT is installed in the 2-CT method as per the manual.

도면.png

 

Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
caimin_pan
Ensign caimin_pan Ensign
Ensign

Posted: ‎2024-09-25 10:14 PM

0 Likes
0
520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-25 10:14 PM

1)You can confirm if the grounding system settings match the corresponding switches?
2) Have you called Schneider Electric hotline for help?
3) Have you updated FW?
4) Can you provide more information? For example, the screenshot below,  event logs and wave form data

caimin_pan_0-1727327588248.pngcaimin_pan_1-1727327613246.png

 

See Answer In Context

Reply
Yan_Zhang
Ensign Yan_Zhang Ensign
Ensign

Posted: ‎2024-09-25 10:42 PM . Last Modified: ‎2024-09-26 09:37 PM

0 Likes
2
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-25 10:42 PM

Hello 2WON,

Could you please provide the part number and serial number for the PCS+? and the SLD of the system include CT installation position.

Did you check the fuses/switches (if exist) on 3 phases?

And please switch to English Language in HMI when you take screenshot. Thanks!

BRs

See Answer In Context

Reply
Replies 4
caimin_pan
Ensign caimin_pan Ensign
Ensign

Posted: ‎2024-09-25 10:14 PM

0 Likes
0
521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-25 10:14 PM

1)You can confirm if the grounding system settings match the corresponding switches?
2) Have you called Schneider Electric hotline for help?
3) Have you updated FW?
4) Can you provide more information? For example, the screenshot below,  event logs and wave form data

caimin_pan_0-1727327588248.pngcaimin_pan_1-1727327613246.png

 

Reply
Yan_Zhang
Ensign Yan_Zhang Ensign
Ensign

Posted: ‎2024-09-25 10:42 PM . Last Modified: ‎2024-09-26 09:37 PM

0 Likes
2
520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-25 10:42 PM

Hello 2WON,

Could you please provide the part number and serial number for the PCS+? and the SLD of the system include CT installation position.

Did you check the fuses/switches (if exist) on 3 phases?

And please switch to English Language in HMI when you take screenshot. Thanks!

BRs

Reply
caimin_pan
Ensign caimin_pan Ensign
Ensign

Posted: ‎2024-09-26 01:52 AM

0 Likes
1
496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-26 01:52 AM

It is not  CT issue, the 3phases currents of load are normal.

@2WON  When did these two warning signs appear? Has it been there all along? Will it disappear?

I will discuss this with PCS+ FW engineer, please give me your feedback. 

Reply
2WON
2WON
Cadet

Posted: ‎2024-10-01 09:29 PM

0 Likes
0
434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-01 09:29 PM

The error on L1 has been present from the beginning. What I want to know is whether the error shown is the correct one that appears when the IT/BP switches are not opened, considering that all IT/BP switches should be opened in the IT grounding system. Since the distance between my office and the installation site is quite far, I need to resolve this in a single visit.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of