Question - Is that correct wiring for ION7650? MV measurement 3PTstar, 2CT L1,L3 - volts mode 4W-Wye

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Question - Is that correct wiring for ION7650? MV measurement 3PTstar, 2CT L1,L3 - volts mode 4W-Wye
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
488
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
jary_svab
jary_svab
Cadet

Posted: ‎2015-01-12 04:37 AM

1 Like
10
2684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-12 04:37 AM

Question - Is that correct wiring for ION7650? MV measurement 3PTstar, 2CT L1,L3 - volts mode 4W-Wye

Typical wiring from Installation guide ION7650

5520

If we use wire the Voltage and Current Inputs like bellow is there any impact for billing and power quality measurement with setting of volts mode = 4W-Wye ? This wiring is not mentioned in Installation guide, but for mesuremnet in MV site are very offten used 3PT(star) and 2CT(L1,L3).

5521

Thank you in advance for estimation and answers.

Tags (3)
  • Tags:
  • for
  • ion7650
  • wiring
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2015-02-06 02:03 PM

1 Like
7
2511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-06 02:03 PM

Short answer: Yes.

The volts mode should always be configured to match how the voltage terminals are connected (on this platform, processing of current channels is not affected by volts mode).

The 2CT configuration shows actually generates the residual current in the CT secondary, so as long as load current only flows on 3 wires (up to one more wire than you have CTs), all readings will be correct (assuming perfectly matched CTs).

The term "balanced" is a little misleading. The residual current generated by the CT secondaries will be a proportional representation of the line current so long as all the residual current is flowing in that line. Technically theis means that the zero-sequence magnidue (only measureable with 3CTs) is near zero. Problems typically arise when load current returns on a 4th neutral conductor or in ground as a fault.

See Answer In Context

Reply
Replies 10
jimbradley
Lt. Commander jimbradley
Lt. Commander

Posted: ‎2015-01-12 09:35 AM

2 Likes
0
2511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-12 09:35 AM

Hi,

I have sen this approached used by utilities in HV and MV installations as CTs for these voltage levels are expensive.

The flaw in using 2 CTs is that the load must be balanced for accurate power and energy results.  The wiring assumes that Ia + Ib + Ic = 0 (vectorally).  Any unbalanced current is missed.  In utility MV distribution the assumption that the load is balanced is often incorrect due to single phase distribution legs.  In environments with harmonic currents such as non linear loads like VFDs, UPSs,, etc. the unbalanced current. can be significant especially in regards to harmonic currents.

Jim

Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2015-02-06 02:03 PM

1 Like
7
2512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-06 02:03 PM

Short answer: Yes.

The volts mode should always be configured to match how the voltage terminals are connected (on this platform, processing of current channels is not affected by volts mode).

The 2CT configuration shows actually generates the residual current in the CT secondary, so as long as load current only flows on 3 wires (up to one more wire than you have CTs), all readings will be correct (assuming perfectly matched CTs).

The term "balanced" is a little misleading. The residual current generated by the CT secondaries will be a proportional representation of the line current so long as all the residual current is flowing in that line. Technically theis means that the zero-sequence magnidue (only measureable with 3CTs) is near zero. Problems typically arise when load current returns on a 4th neutral conductor or in ground as a fault.

Reply
frans-willem
frans-willem
Cadet

Posted: ‎2015-04-06 11:53 PM

0 Likes
6
2511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-06 11:53 PM

Hi All,

Further to this discussion:

Can the ION meter estimate the neutral current given a 3 CT installation?

I'm sceptical about vector calculations as currents waveforms are typically very far from sinusoidal.

Numerical, subcycle waveform addition and RMS calculations should do better but I think the neutral will typically be phase shifted leading to an innacurate estimation.

Any thoughts?

Frans-Willem Vermaak

South Africa

Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2015-04-07 10:29 AM

0 Likes
5
2511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-07 10:29 AM

The ION 7650 can of course perform vector or many other user specified calculations.

The best way to determine the residual neutral current on a 4-wire system with three CTs (especially where harmonics are present) is to sum the three CT secondaries and pass the result through the I4 terminals on the ION7650.

6143

Reply
giuliano
giuliano
Cadet

Posted: ‎2015-04-07 12:05 PM

0 Likes
0
2511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-07 12:05 PM

Estarei ausente do escritório a partir de 06/04/2015 e não retornarei até

16/04/2015.

Responderei à sua mensagem quando retornar.

Em caso de urgência entrar em contato com:

Bruno Galfo (bruno.galfo@schneider-electric.com) ou Sandra Haro

(sandra.haro@schneider-electric.com)

Je serai absent(e) à partir du 20/12/2012 de retour le 07/01/2013.

I'm out of office and will be back on January 7th . My e-mail access will

be limited .

Best regards

Reply
aaron_azzo_com_
Ensign aaron_azzo_com_
Ensign

Posted: ‎2015-06-02 06:50 PM

0 Likes
3
2511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-06-02 06:50 PM

Hi Dan.  Would it not be best practice to use a fourth CT for I4 rather than relying on secondary shorting?  Also, if the S2 is earthed as it's supposed to be for reference, how would that affect the S1's of the three phases being brought together; would this not create a short?

Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2015-06-03 11:32 AM

1 Like
2
2511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-06-03 11:32 AM

This technique of summing CT secondaries (from 2, 3 or 4 CTs) is most commonly used when low price is more important than accuracy.

On a 3-wire system (3 conductors between the source and load), there is no fourth wire in the system to put the fourth CT on... The wiring diagram above effectively uses the meter's I4 terminals to measure the return current in the CT secondary common wire (typically 3 CTs are wired with one wire each plus a shared common wire that is grounded at one point).

There are also special purpose CTs (zero sequence CTs or Earth leakage CTs) that could possibly be used instead - but I'm not sure they have much of an advantage in this situation.

I'm not familiar with the terms "S1" and "S2"? On the ION7650 the S1, S2, S3... S8 terminals are the digital Status Inputs.

Or did you mean the common wire of the CT secondaries? Yes, the CT common (non-dot side of CT output) is grounded at the shorting block for safety - it prevents the CT secondaries from floating to coupled voltages (usually primary-side voltage).

Reply
aaron_azzo_com_
Ensign aaron_azzo_com_
Ensign

Posted: ‎2015-06-03 04:58 PM

0 Likes
0
2511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-06-03 04:58 PM

Hi Dan, thanks for clearing that up.  I was referring to the wye connection, not the delta, which is the one in question; my mistake.

S1 and S2 refer to the high and low (grounded) leg of CTs on the secondary; S2 should always be the earthed terminal.  The main purpose is to ensure a solid reference, rather than referring to itself, which will cause erroneous readings.  Where I was initially going with this was exactly as you said, which is accuracy: if a customer is purchasing a very costly PQ meter (ION7650), holding back on accuracy defeats the purpose of having a PQ meter on their system in the first place.  If four CT's can be used on the system (some utilities do have wye HV:MV transformer), then I think it's best to use them for the sake of accuracy, and the sake of ensuring the high-end meter is installed in a high-end fashion.

Reply
engineer_langfo
Lieutenant JG engineer_langfo
Lieutenant JG

Posted: ‎2015-10-05 03:17 PM

0 Likes
0
2511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-05 03:17 PM

Dan,

Of course; the "other" reason there is no neutral CT is when an ION7650 is retrofitted into an existing installation where there are only three CTs.  We would then have to do a residual current calculation like on the ION73x0 meters using an arithmetic module in the ION7650. 

Can you confirm what algorithm should be programmed into an arithmetic module in order to calculate the residual current?
I am guessing I residual =  I1*cos(I1 angle) + I2*cos(I2 angle) + I3*cos(I3 angle)  ...

.. where I1 is from the power meter module and I1 angle is from the Power Harmonics Module.

Is this valid?

Reply
edward_lim_uon_
Ensign edward_lim_uon_
Ensign

Posted: ‎2016-06-14 01:43 AM

0 Likes
0
2511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-14 01:43 AM

Hello Jaroslav,

Did you end up wiring the 3PT and 2 CT and using 4W mode? Was everything OK?

I am trying to work out the correct way to wire this ABB metering TX to ION8800.

RegardsABB metering TX.png
Edward

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of