Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hi,
Is it possible to use the powertag intended for bus, for cables? I have a 3rd party breaker which is 200A and need to install a powertag for a energy monitoring project.
Best,
Lahiru
Link copied. Please paste this link to share this article on your social media post.
Hi!
Yes it is a rogowski solution, and you can wrap it around cable wires it does not matter if it is busbar og wires.
Link copied. Please paste this link to share this article on your social media post.
Hi!
Can this help you? PowerTag Rope 200A
Link copied. Please paste this link to share this article on your social media post.
Hi Nikolaj,
This installation videos and other material points to this as a solution for bus. But what i need is something for cables. Guess this is a rogowski coil. Just wanted a confirmation that this can be used as a substitute for cable types ct's.
Best,
Lahiru
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.