Hi,
Is it possible to use the powertag intended for bus, for cables? I have a 3rd party breaker which is 200A and need to install a powertag for a energy monitoring project.
Best,
Lahiru
Link copied. Please paste this link to share this article on your social media post.
Hi!
Yes it is a rogowski solution, and you can wrap it around cable wires it does not matter if it is busbar og wires.
Link copied. Please paste this link to share this article on your social media post.
Hi!
Can this help you? PowerTag Rope 200A
Link copied. Please paste this link to share this article on your social media post.
Hi Nikolaj,
This installation videos and other material points to this as a solution for bus. But what i need is something for cables. Guess this is a rogowski coil. Just wanted a confirmation that this can be used as a substitute for cable types ct's.
Best,
Lahiru