Power Meter PM5350-FRAM Error

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Wachirasak
Ensign
Ensign
0 Likes
1
290

Power Meter PM5350-FRAM Error

What is the cause of the error?

FRAM Error


281013.jpg

Tags (3)
1 Reply 1
Ramasamy_N
Commander Commander
Commander

Re: Power Meter PM5350-FRAM Error

Hi Wachirasak,

The FRAM error accrues due to the CRC fail during the file transfer. Please do power cycle for the meter and repeat the firmware upgrade with same DLF configuration, the error will not be there. Let me know if the error is still there.