Position for calibration pulser modules not getting reset on ION meter
While running some tests on a custom ION7550 framework I observed that the "position" of the calibrated pulser module is not getting reset despite having done a master reset on the device.
I would assume the master reset clears out everything (logs, energy, demand, min, max, ect.). But it appears the position on these modules is always remembered.
I am outputting a kWh pulse on R1 (1 kWh= 1pulse -> Kt=1000. I do a master reset, energy registers reset. However when say 0.45kWh accumulates, the module pulses the port.
Is this normal intended behavior?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Matthew,
Did you do resetting when there was load ? If so one second after reset was done you will have energy accumulated for sure.
Yut