Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
We are working with OKKEN panels in a Data Center and are experiencing intermittent communication failures across multiple LV OKKEN skids. The panels operate normally, but communication is randomly lost on different devices without any visible cause. It becomes impossible to establish communication through the RJ45 port, through the communication switch, or even when connecting directly to the affected device. PQM measurements remain correct, but the communication channel stays down. But when we RESTART the PQM the communucation is reestablish again
Link copied. Please paste this link to share this article on your social media post.
Hi @sergiotusen
Based on your description, the issue may be related to excessive network traffic or switch configuration impacting the PM8000 meters’ communication stability.
The PM8000 series includes a communication throttling mechanism that slows down response times if the meter detects too much network traffic. This is designed to protect metering functionality under heavy network load.
Here are some recommendations and considerations:
Switch Configuration
Traffic Management
Local Communication Check
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
PQM 8000 after restart and stablish communication
PQM 8000 with the Communication issues and NOT reading on EPMS
PQM Model
Link copied. Please paste this link to share this article on your social media post.
Hi @sergiotusen
Based on your description, the issue may be related to excessive network traffic or switch configuration impacting the PM8000 meters’ communication stability.
The PM8000 series includes a communication throttling mechanism that slows down response times if the meter detects too much network traffic. This is designed to protect metering functionality under heavy network load.
Here are some recommendations and considerations:
Switch Configuration
Traffic Management
Local Communication Check
Best Regards,
-Mehran
L3 Expert Advanced metering
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.