We are working with OKKEN panels in a Data Center and are experiencing intermittent communication failures across multiple LV OKKEN skids. The panels operate normally, but communication is randomly lost on different devices without any visible cause. It becomes impossible to establish communication through the RJ45 port, through the communication switch, or even when connecting directly to the affected device. PQM measurements remain correct, but the communication channel stays down. But when we RESTART the PQM the communucation is reestablish again
Link copied. Please paste this link to share this article on your social media post.
Hi @sergiotusen
Based on your description, the issue may be related to excessive network traffic or switch configuration impacting the PM8000 meters’ communication stability.
The PM8000 series includes a communication throttling mechanism that slows down response times if the meter detects too much network traffic. This is designed to protect metering functionality under heavy network load.
Here are some recommendations and considerations:
Switch Configuration
Traffic Management
Local Communication Check
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
PQM 8000 after restart and stablish communication
PQM 8000 with the Communication issues and NOT reading on EPMS
PQM Model
Link copied. Please paste this link to share this article on your social media post.
Hi @sergiotusen
Based on your description, the issue may be related to excessive network traffic or switch configuration impacting the PM8000 meters’ communication stability.
The PM8000 series includes a communication throttling mechanism that slows down response times if the meter detects too much network traffic. This is designed to protect metering functionality under heavy network load.
Here are some recommendations and considerations:
Switch Configuration
Traffic Management
Local Communication Check
Best Regards,
-Mehran
L3 Expert Advanced metering