It is not possible to integrate a Xenta Server (9xx, 7xx) to PME. This configuration would require the Xenta Webserver to behave as "Modbus TCP slave device" which is NOT supported.
Refer to the following article: Article #11539 | The Exchange Knowledgebase
The correct solution would be a Modbus RTU Gateway like the Schneider EGX series or the Veris U013-0012.