Hello, I am working with PME 2023, I have created a device within DTE and added additional Digital Input registers. now that I want to create Alarm rules (within Web application) for those inputs, I am not able to set the rules for the new registers created. Only the predefined registers are shown. Can someone help me with this ?
Link copied. Please paste this link to share this article on your social media post.
Hi,
Sometimes it takes time for the web application to recognize the links of a custom measurement for a custom driver.
You may want to enable the PC based logs for these new inputs and let them log for at least one interval - you can disable the logs later as you wish.
This should allow you to see the new measurement in the Web App for selection.
If you still face an issue, I recommend reaching out to your local tech support for further assistance.
Link copied. Please paste this link to share this article on your social media post.
Hi,
Sometimes it takes time for the web application to recognize the links of a custom measurement for a custom driver.
You may want to enable the PC based logs for these new inputs and let them log for at least one interval - you can disable the logs later as you wish.
This should allow you to see the new measurement in the Web App for selection.
If you still face an issue, I recommend reaching out to your local tech support for further assistance.
Link copied. Please paste this link to share this article on your social media post.
Thanks Rafaela for your reply, I was able to solve my issue by enable logs and using the designer.