Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM89M0024 analogue IO module for PM8000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM89M0024 analogue IO module for PM8000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
nigel_greenwave
nigel_greenwave
Mentor

Posted: ‎2020-06-19 02:38 AM

0 Likes
7
3838
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-19 02:38 AM

PM89M0024 analogue IO module for PM8000

Hi,

Is it at all possible to power a 4-20ma or 0-10v sensor from the analogue IO card and not from a external power supply?

We have a situation where it's not possible to install a external power supply, but need to use the analogue IO card for temperature monitoring.

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-06-25 11:10 AM

1 Like
0
3808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-25 11:10 AM

Hello Nigel,

 

If you only have the analog IO card, then correct, will not work.

 

Charles

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
DanL
DanL Champion
Champion

Posted: ‎2020-06-19 12:09 PM

0 Likes
6
3833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-19 12:09 PM

The PM89M0024 is a set of "4-20ma or 0-10v sensor" powered by and physically attached to the PM8000.
One meter can have a maximum of 4 cards attached.
Are you asking about powering additional sensors that are not designed for the PM8000? What is it? What requirements?

 

The other module available is the digital IO module that also contains a 16V wetting source rated for 20mA.
https://www.se.com/ww/en/product/METSEPM89M0024/powerlogic-pm8000---i-o-module---analogue---4-inputs...

Tags (1)
  • Tags:
  • english
Reply
nigel_greenwave
nigel_greenwave
Mentor

Posted: ‎2020-06-19 10:51 PM

0 Likes
5
3828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-19 10:51 PM

Hi Dan,

 

I'm connecting a 4-20ma temperature sensor to the analogue card, but I don't have 0-30v volts available at the sensor or power meter. I was hoping that the analogue card could provide 0-30v dc?

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-06-25 07:51 AM

0 Likes
4
3817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-25 07:51 AM

Hello @nigel_greenwave,

 

The Analog output of the PM8000 is very likely not able to power your sensor. The digital in module has a wetting source that may be able to power the sensor however without knowing anything about this sensor I can not say for sure.

 

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
nigel_greenwave
nigel_greenwave
Mentor

Posted: ‎2020-06-25 08:53 AM

0 Likes
3
3815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-25 08:53 AM

Attached is the sensor that we need to connect

 

 

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-06-25 09:46 AM

0 Likes
2
3813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-25 09:46 AM

Hello @nigel_greenwave 

 

The screenshot shows AC voltage but the install guide shows DC so I will assume DC voltage. What this screenshot does not show is what is the maximum current draw at the different voltage levels assuming 20mA output. The wetting source is 16V so that part is okay, however we need to know what the maximum current draw is before we can say if wetting source can be used.

 

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
nigel_greenwave
nigel_greenwave
Mentor

Posted: ‎2020-06-25 10:13 AM

0 Likes
1
3810
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-25 10:13 AM

Thanks for your feedback Charles,

 

I also cant find the current draw even on the sensor.

However how I understand it, it's only the digital IO card that has the wetting 16V DC, and we only have the analogue IO card available so it wont work?

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-06-25 11:10 AM

1 Like
0
3808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-25 11:10 AM

Hello Nigel,

 

If you only have the analog IO card, then correct, will not work.

 

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore