PM8000 range and FCAS metering

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 range and FCAS metering
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
alannavial
Crewman alannavial Crewman
Crewman

Posted: ‎2022-11-09 08:35 PM

0 Likes
3
2156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-09 08:35 PM

PM8000 range and FCAS metering

My customer, owner of service stations in Australia, has some questions below, please help me to answer these:

 

I am doing some due diligence on the PM8000 range and I see that Schneider has released a manufacturer declaration of conformity for IEC 61557-12:2007.  Is this valid for all PM8000 meters, or just specific versions?

 

Is there an intent to update this declaration to the latest 2018 version of the standard?  Or is there some aspect of the 2018 version the PM8000 does not meet?

 

With regard to the declaration, how is this impacted by CT/VT choices?  Specifically around the frequency measurement accuracy.  The MASS calls for less than or equal to 0.01Hz intrinsic uncertainty for local frequency measurements…..if we take the Class 0.2 accuracy for frequency as per the declaration, this is OK, but I expect this changes if you are using VT’s, but is not impacted by the accuracy of CT’s?

 

Are there specific versions/options of the PM8000 that are required to enable participation in FCAS?

 

I assume that as the PM8000 is storing the frequency values as 32bit Floats, we can meet the 0.0025Hz resolution requirement for both read and stored frequency measurements.

 

Lastly, when taking highspeed data recordings, can we:

  • Trigger off a number of different frequency thresholds within 50ms?
  • Record frequency and power at 50ms for 5 seconds before the event, 10 seconds during the event, and 60 seconds after the event (75s total)?
  • How quickly can the PM8000 recover and start recording the next event (flush high speed registers, reset data recorder, etc)?
  • Is the above impacted by the method of communications to the meter?
  • What happens when a number of events occur in quick succession, say at 2s after event, 15 seconds after, 60 seconds after, etc)?
Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-11-10 12:10 PM

0 Likes
2
2136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-10 12:10 PM

Hello @alannavial ,

 

I cannot answer all your questions but I can speak to some.

If declaration of conformity was limited to specific versions of PM8000 meters, the limitation would be included with declaration.

 

Regarding FCAS, have to looked at https://community.se.com/t5/Metering-Power-Quality/PM8000-Frequency-resolution/m-p/406158#M6418
https://community.se.com/t5/Metering-Power-Quality/ION9000-FCAS-window-monitoring/m-p/403065#M6360

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-11-15 09:21 AM

0 Likes
0
2053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-15 09:21 AM

Hello @alannavial ,

 

This really depends on the settings inside the dat recorder. There are multiple settings that do different things. For more information recommend you look at the ION Reference guide.

 

Depth is the total amount of data the recorder can keep in memory before either FIFO cycled out old data or recorder is full and needs to be reset. This is used the size the memory in non-volatile memory

 

Buffer depth is the number of records to keep in RAM (volatile) memory, This will be some multiple of 1+ # records before trigger + # records after trigger. All data is written to internal buffer before being transferred to long term storage. The number of record sets determines how many triggers before the buffer is full. The recordings can be triggered back to back, however there is some limitations on how fast the meter can transfer to non-volatile memory.

 

Say for example to have 2 records before the trigger and 7 records after. The total set would be 1+2+7 records. If the buffer depth was 20, you could have 2 triggers before the buff was full. If the depth was 500, you would have 50 triggers. More triggers, more time to move data from buffer to non-volatile memory.

 

There are some limits to buffer depth, this buffer is shared with all data and waveform recorders.

 

Before you ask, no I cannot give you any timings for transferring data as this will greatly depend on what else is happening on the meter.

Regarding triggering during a bust logging in progress I do not know for sure the meter's behavior.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-11-10 12:10 PM

0 Likes
2
2137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-10 12:10 PM

Hello @alannavial ,

 

I cannot answer all your questions but I can speak to some.

If declaration of conformity was limited to specific versions of PM8000 meters, the limitation would be included with declaration.

 

Regarding FCAS, have to looked at https://community.se.com/t5/Metering-Power-Quality/PM8000-Frequency-resolution/m-p/406158#M6418
https://community.se.com/t5/Metering-Power-Quality/ION9000-FCAS-window-monitoring/m-p/403065#M6360

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
alannavial
Crewman alannavial Crewman
Crewman

Posted: ‎2022-11-10 03:28 PM

0 Likes
1
2127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-10 03:28 PM

Hi Charles,

 

Thank you very much for the helpful links.  I think that answered most of my customers questions, except now they want to know about the recovery time after an event, see below:

 

The last piece of the puzzle is the recovery time after an event and what happens during multiple events.  I’ve had experience with similar spec (non Schneider) meters that take significant time to recover the HS registers to trigger another recording, etc.  It’s pretty important to understand the limitations, so that we can be aware and manage the impacts.

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-11-15 09:21 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-15 09:21 AM

Hello @alannavial ,

 

This really depends on the settings inside the dat recorder. There are multiple settings that do different things. For more information recommend you look at the ION Reference guide.

 

Depth is the total amount of data the recorder can keep in memory before either FIFO cycled out old data or recorder is full and needs to be reset. This is used the size the memory in non-volatile memory

 

Buffer depth is the number of records to keep in RAM (volatile) memory, This will be some multiple of 1+ # records before trigger + # records after trigger. All data is written to internal buffer before being transferred to long term storage. The number of record sets determines how many triggers before the buffer is full. The recordings can be triggered back to back, however there is some limitations on how fast the meter can transfer to non-volatile memory.

 

Say for example to have 2 records before the trigger and 7 records after. The total set would be 1+2+7 records. If the buffer depth was 20, you could have 2 triggers before the buff was full. If the depth was 500, you would have 50 triggers. More triggers, more time to move data from buffer to non-volatile memory.

 

There are some limits to buffer depth, this buffer is shared with all data and waveform recorders.

 

Before you ask, no I cannot give you any timings for transferring data as this will greatly depend on what else is happening on the meter.

Regarding triggering during a bust logging in progress I do not know for sure the meter's behavior.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of