PM8000 disable alarms, events, logging when generator not operating

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Grant_IPACS
Commander
Commander
0 Likes
3
543

PM8000 disable alarms, events, logging when generator not operating

Hi,

We have some PM8000's on client stand-by generators, we would like to better utilize the logging and alarms, waveform capture, etc.  But right now as it is quite normal for the generators to be off, or ramping down, most of the captured data is at generator stop or start and potentially not worth perusing for analysis, thus the metering alarms are now effectively being ignored and my worry is that real events are also being missed.

Is there a way to only trigger starting any alarms recordings, etc, when the generator is running?  whether that be via digital input, (gen run signal) or possibly even setting a current limit to enable say < 20 Amps?

Regards

Grant

Accepted Solutions
Charles_Murison
Picard Picard
Picard
0 Likes
2
542

Re: PM8000 disable alarms, events, logging when generator not operating

Hello Grant,

 

There are many ways to do things with ION meters, for example, you could connect a status of a digital input to the enable of the sag/swell module. Or use a setpoint module with current input and status output linked to the enable. These are just examples of what can be done.

 

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

3 Replies 3
Charles_Murison
Picard Picard
Picard
0 Likes
2
543

Re: PM8000 disable alarms, events, logging when generator not operating

Hello Grant,

 

There are many ways to do things with ION meters, for example, you could connect a status of a digital input to the enable of the sag/swell module. Or use a setpoint module with current input and status output linked to the enable. These are just examples of what can be done.

 

Charles

L4 Prime for Advanced metering and Utilities
Grant_IPACS
Commander
Commander
0 Likes
1
536

Re: PM8000 disable alarms, events, logging when generator not operating

Thanks @Charles_Murison any practical examples or screenshots you can share?

Regards

Grant
Charles_Murison
Picard Picard
Picard
0 Likes
0
534

Re: PM8000 disable alarms, events, logging when generator not operating

Hello Grant,

 

I do not have any examples I can share.

 

Charles

L4 Prime for Advanced metering and Utilities