There are two PM8000 meters at a site connected to PME.
* One can run the EN50160:2010 report. It can't run EN50160:2000 reports. It has firmware 1.03.01 and template 8000_FAC-PQ_V1.1.0
* One can run the EN50160:2000 report. It can't run EN50160:2010 reports. It has firmware 1.04.03 and template 8000_FAC-PQ_V1.4.0.0.0
What might be the reason for the difference?
Is it typical that PM8000 meters can run one of these EN50160 reports and not the other?
Link copied. Please paste this link to share this article on your social media post.
Hello,
Be sure to backup the database before making any modifications.
No this is not typical, possibly not an issue with the meter itself. In the ION_Network database there is a table that records what versions of meter templates can run the EN501660:2010 rereport. In ION_Network, uder Views, there is one for cfg_ItemValues, if you edit this view you can search for 'EN50160_V2010_Frameworks' and append the template name of the V1.4. Remeber that the name will need the special character between names, examples of names for the V1.1 framework are below.
'8000_FAC-PQ_V1.1.0.0.0·8000_FAC_V1.1.0.0.0·
Link copied. Please paste this link to share this article on your social media post.
Hello,
Be sure to backup the database before making any modifications.
No this is not typical, possibly not an issue with the meter itself. In the ION_Network database there is a table that records what versions of meter templates can run the EN501660:2010 rereport. In ION_Network, uder Views, there is one for cfg_ItemValues, if you edit this view you can search for 'EN50160_V2010_Frameworks' and append the template name of the V1.4. Remeber that the name will need the special character between names, examples of names for the V1.1 framework are below.
'8000_FAC-PQ_V1.1.0.0.0·8000_FAC_V1.1.0.0.0·
Link copied. Please paste this link to share this article on your social media post.
Hi Charles.
Thanks for that answer. You are a legend.
Changing that one value in CFG_ItemValue table fixed it. The relevant ItemID was found in the CFG_Item table.