PM8000 and EN50160:2010 or EN50160:2000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 and EN50160:2010 or EN50160:2000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
swil
Commander swil
Commander

Posted: ‎2019-03-19 11:03 PM . Last Modified: ‎2019-03-19 11:17 PM

0 Likes
2
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-03-19 11:03 PM

PM8000 and EN50160:2010 or EN50160:2000

There are two PM8000 meters at a site connected to PME.

* One can run the EN50160:2010 report. It can't run EN50160:2000 reports. It has firmware 1.03.01 and template 8000_FAC-PQ_V1.1.0

* One can run the EN50160:2000 report. It can't run EN50160:2010 reports. It has firmware 1.04.03 and template 8000_FAC-PQ_V1.4.0.0.0

 

What might be the reason for the difference?

Is it typical that PM8000 meters can run one of these EN50160 reports and not the other?

Tags (2)
  • Tags:
  • en50160
  • pm8000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-03-20 09:45 AM

1 Like
1
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-03-20 09:45 AM

Hello,

 

Be sure to backup the database before making any modifications.

 

No this is not typical, possibly not an issue with the meter itself. In the ION_Network database there is a table that records what versions of meter templates can run the EN501660:2010 rereport. In ION_Network, uder Views, there is one for cfg_ItemValues, if you edit this view you can search for 'EN50160_V2010_Frameworks'  and append the template name of the V1.4. Remeber that the name will need the special character between names, examples of names for the V1.1 framework are below.

 '8000_FAC-PQ_V1.1.0.0.0·8000_FAC_V1.1.0.0.0·

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-03-20 09:45 AM

1 Like
1
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-03-20 09:45 AM

Hello,

 

Be sure to backup the database before making any modifications.

 

No this is not typical, possibly not an issue with the meter itself. In the ION_Network database there is a table that records what versions of meter templates can run the EN501660:2010 rereport. In ION_Network, uder Views, there is one for cfg_ItemValues, if you edit this view you can search for 'EN50160_V2010_Frameworks'  and append the template name of the V1.4. Remeber that the name will need the special character between names, examples of names for the V1.1 framework are below.

 '8000_FAC-PQ_V1.1.0.0.0·8000_FAC_V1.1.0.0.0·

L4 Prime for Advanced metering and Utilities
Reply
swil
Commander swil
Commander

Posted: ‎2019-03-20 08:48 PM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-03-20 08:48 PM

Hi Charles.


Thanks for that answer. You are a legend.

Changing that one value in CFG_ItemValue table fixed it. The relevant ItemID was found in the CFG_Item table.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of