Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 V2.1.0 - Updating to Factory V2.1.0 template if option not selected during .zip upgrade process

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 V2.1.0 - Updating to Factory V2.1.0 template if option not selected during .zip upgrade process
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
swil
swil
Mentor

Posted: ‎2019-07-22 07:18 PM . Last Modified: ‎2019-07-22 07:19 PM

0 Likes
5
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-22 07:18 PM

PM8000 V2.1.0 - Updating to Factory V2.1.0 template if option not selected during .zip upgrade process

Hi, 

 

If the Factory V2.1.0 Template option is not selected during the upgrade process, is there any way to do it at a later time?

It seems that after the upgrade is completed, the upgrade window in ION setup no longer allows for .zip folder upgrade type and the window that offers the V2.1.0 Template (desired screen I can no longer access attached).

 

Failed attempts to get the meter to not display the messy extra modules grouping window include:

* Copy .dcf file from a device that had the correct template

* Copy and rename .cfg file that was displaying as required in designer to config/diagrams/nd

Attachments
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-07-24 11:19 AM

0 Likes
2
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-24 11:19 AM

In the meter, there is no organization of the modules into frameworks, all modules are grouped by type as you would see in ION Setup Advanced configuration. In designer, the .cfg file stores the diagram view. However this information is not reset if the meter's template changes. Designer will do a delta between what is in the .cfg file and what is on the meter. So if the cfg file has the module and currently in folder X, changing the template will not change this to now show in Folder Y in designer. You would have to remove (or delete with backup) the .cfg file for the meter in the nd folder and have designer rebuild it.

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 5
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-07-23 09:02 AM

1 Like
4
2147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-23 09:02 AM

Hello Swil,

 

I am a little confused, are you having trouble with the meter or with designer? That is to say, if not using designer would you be having trouble?

 

Your first question " is there any way to do it at a later time?" direct answer is yes, you would need to have the ,dcf file extracted from the zip folder and placed in a location you can access later with ION Setup.

 

I would be a little careful with copying dcf files from other meters. When possible, try to keep the template aligned to the firmware version. Doing this will ensure you have all features available from the version of firmware.

L4 Prime for Advanced metering and Utilities
Reply
swil
swil
Mentor

Posted: ‎2019-07-23 04:56 PM

0 Likes
3
2145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-23 04:56 PM

Hi Charles,

This is a meter that we use for development, and when opened in designer 100+ modules are jumbled in a grid in the other modules grouping window. This may be a meter question. Should I post the question there?

 

I tried copying the dcf file from a V2.1.0 PM8000 meter that is configured correctly with the correct template (to this V2.1.0 PM8000, seemingly without the template), but it didn't work.

 

Previously I thought the .cfg file controlled the location of modules as they are displayed in Designer. Now I'm not so sure.

 

Just looked in Ion Setup. The default template and template displayed in both meters are the same in the template/save to PC window. This implies that the template has been set to the updated template, although designer still doesn't know where the extra modules should go.

 

 

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-07-24 11:19 AM

0 Likes
2
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-24 11:19 AM

In the meter, there is no organization of the modules into frameworks, all modules are grouped by type as you would see in ION Setup Advanced configuration. In designer, the .cfg file stores the diagram view. However this information is not reset if the meter's template changes. Designer will do a delta between what is in the .cfg file and what is on the meter. So if the cfg file has the module and currently in folder X, changing the template will not change this to now show in Folder Y in designer. You would have to remove (or delete with backup) the .cfg file for the meter in the nd folder and have designer rebuild it.

L4 Prime for Advanced metering and Utilities
Reply
swil
swil
Mentor

Posted: ‎2019-07-24 04:01 PM

0 Likes
1
2139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-24 04:01 PM

Thanks Charles.

I deleted the .cfg file and opened meter in designer rebuild it.

 

Funny thing is, designer didn't rebuild a .cfg file and place it in the C:\Program Files (x86)\Schneider Electric\Power Monitoring Expert\config\diagrams\nd folder.  There is no File named GroupName.DisplayName[ME-serial].cfg in this folder now. 

 

I can add modules to the meter framework, save in designer and reopen the meter (in designer) to view the new custom framework. 

 

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-07-25 09:57 AM

1 Like
0
2134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-25 09:57 AM

I would search for the meter's serial number, some parts of PME will use system name, others display name.

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore