New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Connecting meters with 3 RS-485 terminals to meters with 4 RS-485 terminals
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2019-07-2905:38 PM
Connecting meters with 3 RS-485 terminals to meters with 4 RS-485 terminals
Hi,
We are looking to install a serial string with PM5350s, iEM3150s and iEM3350s. The customer has asked if shielded twisted pair is acceptable for the RS-485 connections.
Is it correct to specify Beldin 9841 (or equivalent) to daisy chain the the RS-485 meter connections, leaving the shield terminal unused on the meters where 4 terminals are available (0V, shield, D0- and D0+)?
(Should the cable shield conductor be terminated to the shield connection on meters with three RS-485 terminals, terminated to the 0V connection of meters with 4 available RS-485 terminals, and grounded at a single point?)
Link copied. Please paste this link to share this article on your social media post.
2019-07-3010:01 AM
Hello Swil,
"When wiring these older devices along with newer devices, the shield conductor of the cable should be landed on the 0V terminal of the newer device. This will leave the "shield" connection on the newer devices not connected which is fine."
Link copied. Please paste this link to share this article on your social media post.
2019-07-3010:01 AM
Hello Swil,
"When wiring these older devices along with newer devices, the shield conductor of the cable should be landed on the 0V terminal of the newer device. This will leave the "shield" connection on the newer devices not connected which is fine."