PM8000 - Neutral current calculation

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
DK-Michael
Commander Commander
Commander
0 Likes
1
347

PM8000 - Neutral current calculation

Hi

 

I have a customer with quite a few PM8000's installed. They replaced a lot of PM500 with PM8000, so in many cases they do not have a 4th CT installed for the neutral conductor.

Is there a way to get the PM8000 to calculate the neutral current when we are not measurering it?

 

Best regards, Michael

________________________________
Michael Johansen
Solution Architect
M +4528991535
E michael.johansen@se.com
LinkedIn https://www.linkedin.com/in/mich4el/
Tags (3)

Accepted Solutions
Charles_Murison
Picard Picard
Picard

Re: PM8000 - Neutral current calculation

Hello,

 

Have you looked at the Residual Current Measurement section of the Install and commisioning?

 

PM8000_In.png

L4 Prime for Advanced metering and Utilities

See Answer In Context

1 Reply 1
Charles_Murison
Picard Picard
Picard

Re: PM8000 - Neutral current calculation

Hello,

 

Have you looked at the Residual Current Measurement section of the Install and commisioning?

 

PM8000_In.png

L4 Prime for Advanced metering and Utilities