Bonjour,
une fois de plus j'ai un client (EDF) qui me demande de ne pas afficher les intensités en kA mais en A
la même chose pour la puissance, il me demande des kW, pas des MW.
J'ai trouvé une procédure pour créer un écran personnalisé qui affiche des A et des kW;
cela fonction très bien.
J'ai trouvé également une autre procédure pour modifier directement les pages de mesures de bases.
J'utilise IONSEtup mais dans le menu Display Modules j'ai une page vide à droite.
Je ne dois pas avoir le bon mot de passe.
Quelqu'un peut me le fournir?
Merci d'avance
Annotation 2021-12-15 094356.jpg
Link copied. Please paste this link to share this article on your social media post.
Bonjour @Olivier_GARAULT ,
Please ask any question in English on the Exchange Community.
This is not an issue. If you can access this screen, it means you have the correct password for your PM8000.
I see you are in Advanced mode, then you can directly create a new ION Display Module. Right click on the blank space -> Insert module.
Then double click on the new create "Display 1" ION Display Module.
All information to set up the Display Modules are below:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Bonjour @Olivier_GARAULT ,
Please ask any question in English on the Exchange Community.
This is not an issue. If you can access this screen, it means you have the correct password for your PM8000.
I see you are in Advanced mode, then you can directly create a new ION Display Module. Right click on the blank space -> Insert module.
Then double click on the new create "Display 1" ION Display Module.
All information to set up the Display Modules are below:
Regards,