Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 - Badger Meter reading Issues

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 - Badger Meter reading Issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
mmolina_advance
mmolina_advance
Explorer

Posted: ‎2020-05-12 06:12 AM

0 Likes
3
2686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-12 06:12 AM

PM8000 - Badger Meter reading Issues

We have a PM8000 and a badger meter (Recordall) connected to a PM8000 onboard input . We have not been able to see a single pulse in the meter input. The badger meter has an external power supply and a pull up resistor. Any suggestions?

 

Thanks 

Labels
  • Labels:
  • PM8000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
DanL Champion
Champion

Posted: ‎2020-05-18 01:48 PM

0 Likes
0
2672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-18 01:48 PM

Do you know the Badger model and or specifications?
Is it something like this?
https://www.badgermeter.com/resources/6a7dbf57-f692-4bbc-a25f-c8b537ab9e31/recordall%20transmitter%2...
The above device also requires an external supply and resistance.
-Max voltage for pulse output 30V
-Max current for pulse output 1mA,

Unfortunately 1mA is also very near the minimum required current for the PM8240 digital inputs.
If this is your case, you cannot use a simple external pull-up topology and will have to "tune" the series resistance...

Just to confirm, you have one pulse output and one external supply connected to one PM8240 onboard digital input (eg S1)?

What are the specs of your external supply voltage?

For example asuming a single device and the output specs listed in the above link:

With an external supply: 24Vdc, rated >= 0.1 Watt
Use a series resistor between 20 kOhm and 35 kOhm (rated for >= 1/16W)


With an external supply: 12Vdc, rated >= 0.1 Watt
Use a series resistor between 8 kOhm and 15 kOhm (rated for >= 1/16W)


With an external supply: 5Vdc, rated >= 0.1 Watt
Use a series resistor between 1 kOhm and 3 kOhm (rated for >= 1/16W)

See Answer In Context

Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-05-12 05:13 PM . Last Modified: ‎2022-10-19 02:20 AM

1 Like
1
2683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-12 05:13 PM

Hello @mmolina_advance 

 

looks like this is the same questions as your post https://community.se.com/t5/Power-Metering/PM8000-Onboard-pulse-Input-for-water/td-p/196430

 

Correct?

Charles

 

L4 Prime for Advanced metering and Utilities
Reply
mmolina_advance
mmolina_advance
Explorer

Posted: ‎2020-05-18 04:38 AM

0 Likes
0
2678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-18 04:38 AM

yes..

Reply
DanL
DanL Champion
Champion

Posted: ‎2020-05-18 01:48 PM

0 Likes
0
2672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-18 01:48 PM

Do you know the Badger model and or specifications?
Is it something like this?
https://www.badgermeter.com/resources/6a7dbf57-f692-4bbc-a25f-c8b537ab9e31/recordall%20transmitter%2...
The above device also requires an external supply and resistance.
-Max voltage for pulse output 30V
-Max current for pulse output 1mA,

Unfortunately 1mA is also very near the minimum required current for the PM8240 digital inputs.
If this is your case, you cannot use a simple external pull-up topology and will have to "tune" the series resistance...

Just to confirm, you have one pulse output and one external supply connected to one PM8240 onboard digital input (eg S1)?

What are the specs of your external supply voltage?

For example asuming a single device and the output specs listed in the above link:

With an external supply: 24Vdc, rated >= 0.1 Watt
Use a series resistor between 20 kOhm and 35 kOhm (rated for >= 1/16W)


With an external supply: 12Vdc, rated >= 0.1 Watt
Use a series resistor between 8 kOhm and 15 kOhm (rated for >= 1/16W)


With an external supply: 5Vdc, rated >= 0.1 Watt
Use a series resistor between 1 kOhm and 3 kOhm (rated for >= 1/16W)

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore