PM8000 Alarming & Data Export

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Alarming & Data Export
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
SekherNK
SekherNK Cadet
Cadet

Posted: ‎2022-02-08 06:54 PM

1 Like
3
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-08 06:54 PM

PM8000 Alarming & Data Export

Hi,

 

I have a few questions regarding exporting of alarms and datalogs from PM8240.

 

In a site without PME, can PM8000 send alarms and data logs to a 3rd party system (for eg: BMS or SCADA)?

What is the format of the datalog native export?

What are the comms protocol that PM8000 supports to export the data to such 3rd party systems(e.g FTP, Modbus etc)?

 

Thanks,

Sekher

 

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-02-09 04:41 PM

2 Likes
2
2136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-09 04:41 PM

Hello @SekherNK ,

 

Regarding datalogs there are only 2 ways to export from the meter. The first is to use propriety protocol called ION with software such as ION Setup, Power Monitoring Expert or Power Operation. 

 

The second option is with a module called Log Export module. Refer to ION Reference for more details. In Summary the meter will send email with log data attached as an xml file.

 

It may be possible to transfer Alarm state with modbus however alarm data that you would see from meter's front panel only supported with ION protocol.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-02-09 04:41 PM

2 Likes
2
2137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-09 04:41 PM

Hello @SekherNK ,

 

Regarding datalogs there are only 2 ways to export from the meter. The first is to use propriety protocol called ION with software such as ION Setup, Power Monitoring Expert or Power Operation. 

 

The second option is with a module called Log Export module. Refer to ION Reference for more details. In Summary the meter will send email with log data attached as an xml file.

 

It may be possible to transfer Alarm state with modbus however alarm data that you would see from meter's front panel only supported with ION protocol.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
ausfrosty
Crewman ausfrosty
Crewman

Posted: ‎2022-10-10 11:27 PM

0 Likes
1
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-10 11:27 PM

Hi Charles,

 

Following on from this I have a PM8000 setup and have configured it to send emails to a local SMTP server (in this case I have setup Mailslurper on a local machine in same subnet as meter) when frequency events are recorded.

 

The emails are getting sent however the emails being received by Mailslurper do not have an XML file attached. They instead have mainly timestamps in them as per the screenshot. The data recorders setup to be captured have Freq, Voltage and kW from Power Meter module. If I do a manual Data Recorders Collect through Ion Setup Assistant I can see that data recorder is capturing data correctly in the xml file.

 

This may be an issue with how Mailslurper decodes the emails but was wondering if there is anything I should check on the PM8000 configuration side to make sure the data is attached as an XML file? In particular potentially in the Log Export modle under 'Setup Registers' there is a field 'Attachment Extention' which defaults to MMA.

 

Finally when configuring an smtp email send on a PM8000 can credentials be added so that a secure email is sent?

Attachments
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-10-11 02:00 PM

0 Likes
0
2005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-11 02:00 PM

Hello @ausfrosty 

 

"when configuring an smtp email send on a PM8000 can credentials be added so that a secure email is sent?" No only simple SMTP is supported at this time.

 

"anything I should check on the PM8000 configuration side to make sure the data is attached as an XML file?" Should not have to. Note that file extension may be .mma, however the contents of the file will be xml. I have never used that mail program so I do not know what is done with attachments.

 

I have done packet capture files in the past so I know the data is sent from meter to SMTP server as an attached file. 

 

Regards

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of