Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 Alarm Acknowledge

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Alarm Acknowledge
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Hyeontae-Song
Hyeontae-Song
Explorer

Posted: ‎2022-09-27 07:50 PM

2 Likes
4
2476
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-27 07:50 PM

PM8000 Alarm Acknowledge

Is it possible to delete past alarm history from PM8000 meter?

 

 

If I Acknowledge Alarm for PM8000 in Power Monitoring Expert, can I make Alarm Acknowledge applied to PM8000 Local Device? (automatically applied)

 

Best Regard.

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
DanL Champion
Champion

Posted: ‎2022-10-03 02:17 PM . Last Modified: ‎2022-10-03 02:21 PM

2 Likes
0
2418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-03 02:17 PM

It's worth noting that the term "Alarms" in the context of PME is a separate and distinctly different list from the "Alarms" visible only on the front panel display of the PM8000.

The list of "Alarms" visible in PME are maintained in the PME database and are (mostly) comprised of downloaded EventLog entries from the PM8000 (and the EventLogs of other devices connected to PME).

The list of "Alarms" visible on the front panel display of the PM8000 is a list separate and distinct from the meter's EventLog (though most Alarms usually have one or more corresponding Event entries). The list of "Historical Alarms" and "Active Alarms" visible only on the PM8000 display can only be acknowledged via the display interface on the respective screen.

The list of "Alarms" visible in the PME database can only be acknowledged with PME.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-10-03 02:09 PM

2 Likes
3
2424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-03 02:09 PM

Hello @Hyeontae-Song ,

 

To your second question, "can I make Alarm Acknowledge applied to PM8000 Local Device?" The answer is no.

 

The first question about "delete past alarm history" is a loaded question. The event log on a meter can be cleared, the front panel alarm log cannot. Easiest way to clear a meter's event log is to change the depth, changing this number will clear the log.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
DanL
DanL Champion
Champion

Posted: ‎2022-10-03 02:17 PM . Last Modified: ‎2022-10-03 02:21 PM

2 Likes
0
2418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-03 02:17 PM

It's worth noting that the term "Alarms" in the context of PME is a separate and distinctly different list from the "Alarms" visible only on the front panel display of the PM8000.

The list of "Alarms" visible in PME are maintained in the PME database and are (mostly) comprised of downloaded EventLog entries from the PM8000 (and the EventLogs of other devices connected to PME).

The list of "Alarms" visible on the front panel display of the PM8000 is a list separate and distinct from the meter's EventLog (though most Alarms usually have one or more corresponding Event entries). The list of "Historical Alarms" and "Active Alarms" visible only on the PM8000 display can only be acknowledged via the display interface on the respective screen.

The list of "Alarms" visible in the PME database can only be acknowledged with PME.

Tags (1)
  • Tags:
  • english
Reply
AbhaySingh
AbhaySingh Explorer
Explorer

Posted: ‎2025-03-20 01:42 AM . Last Modified: ‎2025-03-20 01:44 AM

0 Likes
1
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-20 01:42 AM

Hi @Charles_Murison , 

But why we cannot clear/empty "historical Alarms" display as shown below image? Those alarms surely get stored somewhere in the ION Modules. What's the challenges we cannot clear all historical alarms on Front display.  
I tried to check in ION Setup (advanced mode) for all modules but did not find where those historical alarms exist. Is it inside the meter onboard memory which cannot access via ION Setup>modules ?


AbhaySingh_0-1742459885227.png

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-03-20 07:32 AM

0 Likes
0
1433
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-20 07:32 AM

Hello @AbhaySingh ,
You have a loaded question. The event log is controlled by the event log controller module, this module has very few setting registers, depth and threshold. If you change the depth, the meter will need to change the memory therefor you will clear the event log. The front panel historical alarms are not the same as the event log. The historical alarms are in a different section of memory that you cannot access via ION Setup or ION modules.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore