PM8000 Alarm Acknowledge

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Alarm Acknowledge
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Hyeontae-Song
Ensign Hyeontae-Song
Ensign

Posted: ‎2022-09-27 07:50 PM

2 Likes
4
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-27 07:50 PM

PM8000 Alarm Acknowledge

Is it possible to delete past alarm history from PM8000 meter?

 

 

If I Acknowledge Alarm for PM8000 in Power Monitoring Expert, can I make Alarm Acknowledge applied to PM8000 Local Device? (automatically applied)

 

Best Regard.

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2022-10-03 02:17 PM . Last Modified: ‎2022-10-03 02:21 PM

2 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-03 02:17 PM

It's worth noting that the term "Alarms" in the context of PME is a separate and distinctly different list from the "Alarms" visible only on the front panel display of the PM8000.

The list of "Alarms" visible in PME are maintained in the PME database and are (mostly) comprised of downloaded EventLog entries from the PM8000 (and the EventLogs of other devices connected to PME).

The list of "Alarms" visible on the front panel display of the PM8000 is a list separate and distinct from the meter's EventLog (though most Alarms usually have one or more corresponding Event entries). The list of "Historical Alarms" and "Active Alarms" visible only on the PM8000 display can only be acknowledged via the display interface on the respective screen.

The list of "Alarms" visible in the PME database can only be acknowledged with PME.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-10-03 02:09 PM

2 Likes
3
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-03 02:09 PM

Hello @Hyeontae-Song ,

 

To your second question, "can I make Alarm Acknowledge applied to PM8000 Local Device?" The answer is no.

 

The first question about "delete past alarm history" is a loaded question. The event log on a meter can be cleared, the front panel alarm log cannot. Easiest way to clear a meter's event log is to change the depth, changing this number will clear the log.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2022-10-03 02:17 PM . Last Modified: ‎2022-10-03 02:21 PM

2 Likes
0
1148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-03 02:17 PM

It's worth noting that the term "Alarms" in the context of PME is a separate and distinctly different list from the "Alarms" visible only on the front panel display of the PM8000.

The list of "Alarms" visible in PME are maintained in the PME database and are (mostly) comprised of downloaded EventLog entries from the PM8000 (and the EventLogs of other devices connected to PME).

The list of "Alarms" visible on the front panel display of the PM8000 is a list separate and distinct from the meter's EventLog (though most Alarms usually have one or more corresponding Event entries). The list of "Historical Alarms" and "Active Alarms" visible only on the PM8000 display can only be acknowledged via the display interface on the respective screen.

The list of "Alarms" visible in the PME database can only be acknowledged with PME.

Tags (1)
  • Tags:
  • english
Reply
AbhaySingh
Crewman AbhaySingh Crewman
Crewman

Posted: ‎2025-03-20 01:42 AM . Last Modified: ‎2025-03-20 01:44 AM

0 Likes
1
174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-20 01:42 AM

Hi @Charles_Murison , 

But why we cannot clear/empty "historical Alarms" display as shown below image? Those alarms surely get stored somewhere in the ION Modules. What's the challenges we cannot clear all historical alarms on Front display.  
I tried to check in ION Setup (advanced mode) for all modules but did not find where those historical alarms exist. Is it inside the meter onboard memory which cannot access via ION Setup>modules ?


AbhaySingh_0-1742459885227.png

 

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-03-20 07:32 AM

0 Likes
0
162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-20 07:32 AM

Hello @AbhaySingh ,
You have a loaded question. The event log is controlled by the event log controller module, this module has very few setting registers, depth and threshold. If you change the depth, the meter will need to change the memory therefor you will clear the event log. The front panel historical alarms are not the same as the event log. The historical alarms are in a different section of memory that you cannot access via ION Setup or ION modules.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of