Hi there,
Could anyone clarify the specific accuracy figures of the PM8000 with respect to its standard-speed and high-speed frequency measurements?
The technical datasheet refers to "Class 0.2 as per IEC 61557-12". Can this be expressed in more specific engineering terms?
Much obliged
Richard
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Richard
The PM8000 user manual specifies Measurement accuracy for Frequency: +/- 0.02%, IEC 61557-12 Class 0.2
So the accuracy is +/- 0.02%
Hope this helps,
Alana
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thanks Alana