Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM800 and PM5350 meters - Netural connections causing problems with readings

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM800 and PM5350 meters - Netural connections causing problems with readings
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
sesa207714_brid
sesa207714_brid Leader
Leader

Posted: ‎2016-02-29 10:52 AM

0 Likes
2
1781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-29 10:52 AM

PM800 and PM5350 meters - Netural connections causing problems with readings

Hi,

We currently have a customer who is complaining about some issues relating to the PM800, PM5350 meters, and neutral connections. Below is some detail on it. Unfortunately we do not have drawings for this, as the customer has been making changes on site, on the fly and hasn't documented any of this.

  • Board has a combination of PM850 and PM5350 meters for different outgoing feeders on the board.
  • PM850 have a UPS supply to allow them to maintain communications when a power outage occurs, and the transfer from mains to gen hasn't occurred yet.
  • Customer installed PM850 meters without a neutral connection. Neutral connection was installed for PM5350 meters.
  • Line to Neutral readings were off so one of our engineers recommended adding neutral wiring to the PM850 meters. PM5350 meters were reading correctly according to the customer
  • Once the neutral was added to the PM850 meters the readings for the PM5350 have gone bad according to the customer. (No more info on how they have gone bad. Unfortunately the customer did not mention this until after we had flown out from the site).

My strong feeling is that the customer has wired something incorrectly, but they are quite a hostile customer and I would like to know if this has been encountered before? Previously they have been quite aggressive when we asked them to investigate their own work unless we could definitively prove our hardware was infallible.

Thanks for all of your assistance with this issue, and apologies for the lack of information available.

Regards,

Martin

Tags (2)
  • Tags:
  • pm5350
  • pm800
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Yut
Yut
Leader

Posted: ‎2016-03-01 08:20 PM

0 Likes
1
1736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-01 08:20 PM

Seem to be a delta system,isn't it ? If delta set meter to delta.

See Answer In Context

Reply
Replies 2
Yut
Yut
Leader

Posted: ‎2016-03-01 08:20 PM

0 Likes
1
1736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-01 08:20 PM

Seem to be a delta system,isn't it ? If delta set meter to delta.

Reply
sesa207714_brid
sesa207714_brid Leader
Leader

Posted: ‎2016-03-02 12:36 PM

0 Likes
0
1736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-02 12:36 PM

Hi Yut,

Thanks for that. Passed it along to the board builder onsite.

Regards,

Martin

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore