Hi, I’m using modscan to communicate with PM5560, the setting in modscan is same with PM5560 such as baudrate: 9600, parity: None, ID: 1. Connection is successful. Reference from Modbus register list, I check current A at address 3000, function code 4 but reading is 0, it is not matching with actual. How can I solve this issue? Thanks
Link copied. Please paste this link to share this article on your social media post.
Hi @HuyDoan,
Could you please show the configuration you are using in Modscan? Make sure to select 03:HOLDING REGISTER and set the proper device ID.
Link copied. Please paste this link to share this article on your social media post.
I believe all PM5000 registers are read with function code 3 (Read Holding Register). I'm not sure this is called out in the register list itself.
Link copied. Please paste this link to share this article on your social media post.
Hi, maybe this can help you.
Link copied. Please paste this link to share this article on your social media post.
Hi @HuyDoan,
Could you please show the configuration you are using in Modscan? Make sure to select 03:HOLDING REGISTER and set the proper device ID.