Is it possible to get leakage Current from Powertag if we mount PowerTag on RCCB Device?
Link copied. Please paste this link to share this article on your social media post.
Hi @NishitShah
If you are inquiring whether you can obtain leakage current measurements from the PowerTag when it is mounted on an RCCB device, the answer is no. It will measure the phase voltages/current and power values, but not the residual current.
If your concern pertains to the possibility of the PowerTag causing a leakage current when mounted in an RCCB, please note that there won't be any leakage current if it is properly wired according to the instruction sheet.
Link copied. Please paste this link to share this article on your social media post.
Hi @NishitShah
If you are inquiring whether you can obtain leakage current measurements from the PowerTag when it is mounted on an RCCB device, the answer is no. It will measure the phase voltages/current and power values, but not the residual current.
If your concern pertains to the possibility of the PowerTag causing a leakage current when mounted in an RCCB, please note that there won't be any leakage current if it is properly wired according to the instruction sheet.