New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
PM5560 energy count reset
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2023-03-1608:48 AM
PM5560 energy count reset
Hi everyone!
A customer's PM5560 meter has restarted the energy count. This device has been installed just 4 months ago and it happened when the energy had a value that didn`t reach the limit of the meter.
Please find attached the register downloaded from ION Setup.
Link copied. Please paste this link to share this article on your social media post.
2023-03-1608:51 AM
Hello @Veronika1 , When I look at the screenshot I see that there is a big gap in time. Do you know what happened to the meter during this time? Possible the meter's energy was reset? Roll over is just 1 way the energy can reset.
Link copied. Please paste this link to share this article on your social media post.
2023-03-1612:17 PM
Hello, Charles!
Yes, there is a data gap. We're not sure what could happened that day. The customer said that nobody has access to this meter and there's no way that someone could do any change on it.
I forgot to say that few weeks before this happened, the CTs relation config of this meter changed with no reason.
They have 4 PM5560 meters on their plant, installed at the same time and this is the only one that presents this kind of issues.