PM5560 display Pulse counts and Total Usage on the front display and the webpage

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
sesa74337_bridg
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
380

PM5560 display Pulse counts and Total Usage on the front display and the webpage

Hi, All,

If we are using PM5560 to do the water meter pulse count, can either the meter front display or the web page shows the number of pulses? Our customer would like to use PM5560 meters for monitoring Energy and Water usage, the basic requirements is the total pulses and calculated water usage (Pulse weight x total no. of pulses) not only be displayed in PME, but also on the remote meter display and the meter webpage. Could you please confirm if the meter can meet the requirements? If not, will that be in the development path?

Thanks a lot,

James

Attachments

Accepted Solutions
Usha
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
322

Re: PM5560 display Pulse counts and Total Usage on the front display and the webpage

Hi James,

Have you considered using "Input Metering" to meet the requirement?  Please review the user guide: http://download.schneider-electric.com/files?p_File_Id=791779033&p_File_Name=HRB1684301-02.pdf     Section labeled "Input Metering".

The information is viewable from the meters HMI.

Meter’s input metering channels count pulses received from the digital inputs assigned to that channel. The incoming pulses are used in calculating and measuring consumption data (e.g., BTU, kWh, L, kg). Each channel must have the following values configured to match the pulse data:


• Pulse Weight: the pulses per unit value.

• Unit Code: the unit of measure associated with the monitored value.

• Demand Code: for time-based values (such as kWh), this provides the associated demand units (kW) for demand calculations; for other values (such as kg), this can

   be configured to provide rate information (kg/h or kg/s).

• Mode: Whether pulse counting based on full pulses or transitions.

For example, if each complete pulse represents 125 Wh, you can configure for Wh

pulsing as follows:

• Pulse Weight = pulses/Wh = 1/125 = 0.008

• Unit Code = Wh

• Demand Code = kW (this is automatically set)

• Mode = pulse.

Please refer the user guide for more information.

With Regards,

Usha

Usha M R

See Answer In Context

1 Reply 1
Usha
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
323

Re: PM5560 display Pulse counts and Total Usage on the front display and the webpage

Hi James,

Have you considered using "Input Metering" to meet the requirement?  Please review the user guide: http://download.schneider-electric.com/files?p_File_Id=791779033&p_File_Name=HRB1684301-02.pdf     Section labeled "Input Metering".

The information is viewable from the meters HMI.

Meter’s input metering channels count pulses received from the digital inputs assigned to that channel. The incoming pulses are used in calculating and measuring consumption data (e.g., BTU, kWh, L, kg). Each channel must have the following values configured to match the pulse data:


• Pulse Weight: the pulses per unit value.

• Unit Code: the unit of measure associated with the monitored value.

• Demand Code: for time-based values (such as kWh), this provides the associated demand units (kW) for demand calculations; for other values (such as kg), this can

   be configured to provide rate information (kg/h or kg/s).

• Mode: Whether pulse counting based on full pulses or transitions.

For example, if each complete pulse represents 125 Wh, you can configure for Wh

pulsing as follows:

• Pulse Weight = pulses/Wh = 1/125 = 0.008

• Unit Code = Wh

• Demand Code = kW (this is automatically set)

• Mode = pulse.

Please refer the user guide for more information.

With Regards,

Usha

Usha M R