Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

【PM5560】Starting Current and Accuracy of PM5560

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • 【PM5560】Starting Current and Accuracy of PM5560
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
292
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
71
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Miyai
Lieutenant JG Miyai
Lieutenant JG

Posted: ‎2023-07-05 07:26 PM

0 Likes
4
347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-05 07:26 PM

【PM5560】Starting Current and Accuracy of PM5560

Hello 

 

 

I need advice on whether my understanding of the current measurement of PM5560 is correct.

 

The minimum value for current measurement is 5 mA.

However, 5-49mA cannot guarantee the specified accuracy.

The range in which the accuracy of the specified can be maintained is from 50 mA to 10 A.

 

Is the above idea correct?

I would like to confirm the above as the explanation differs from the ION9000 and other manuals.

 

Miyai_0-1688610298117.png

 

 

Best regards,

Miyai

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Commander Ramasamy_N Commander
Commander

Posted: ‎2023-07-07 02:15 AM

1 Like
1
312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-07 02:15 AM

Hi @Miyai 

The PM5500 starting current is 0.1% of nominal current (5mA) which will not claim any accuracy for this range 0.1% to 1%. (5mA to 50mA) in the standards like IEC62053-22 that we comply. 

Ramasamy_N_0-1688721238201.png

The 50mA to 250mA test points will have ±0.4% allowed error even for Class 0.2 meters. 

 

Regards, 

Ramasamy N 

See Answer In Context

Reply
Replies 4
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-07-06 09:51 AM

0 Likes
1
332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-06 09:51 AM

Hello @Miyai ,

 

When you say "explanation differs from the ION9000 and other manuals." What in particular are you referring to in the ION9000 manual?

 

If you are saying the starting current for ION9000 is different than PM5560, this could be explained that these are different meters with different nominal currents.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Miyai
Lieutenant JG Miyai
Lieutenant JG

Posted: ‎2023-07-06 05:02 PM

0 Likes
0
324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-06 05:02 PM

Hello @Charles_Murison 

 

ION9000 manual was described below.

I understand because the ”accuracy range” is clearly stated.

Miyai_0-1688687215751.png

 

However, I do not understand exactly what the PM5500 manual describes.

Is it correct to assume that the area marked below is the accuracy range?

Miyai_1-1688687423071.png

 

I would like to confirm this just to be sure, as I have received an inquiry from a client.

 

Best regards,

Miyai

Reply
Ramasamy_N
Commander Ramasamy_N Commander
Commander

Posted: ‎2023-07-07 02:15 AM

1 Like
1
313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-07 02:15 AM

Hi @Miyai 

The PM5500 starting current is 0.1% of nominal current (5mA) which will not claim any accuracy for this range 0.1% to 1%. (5mA to 50mA) in the standards like IEC62053-22 that we comply. 

Ramasamy_N_0-1688721238201.png

The 50mA to 250mA test points will have ±0.4% allowed error even for Class 0.2 meters. 

 

Regards, 

Ramasamy N 

Reply
Miyai
Lieutenant JG Miyai
Lieutenant JG

Posted: ‎2023-07-11 05:15 PM

0 Likes
0
251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-11 05:15 PM

Hi @Ramasamy_N 

 

I understand.
Thanks for your advice.

 

 

Best regards,

Miyai

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc