Would there be any reason that a PM5560 fails to update an IP address from the communications settings screen?
The PM5560 previously communicated with PME but now has IP address 255.255.255.255.
Upon IP address change and save, IP reverts back to 255.255.255.255.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Have a look at FAQ FA239202
Google -> "Schneider FAQ FA239202" (without quotes)
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi, Can you provide a link to the resolution, I have searched google for this but unfortunately, there is nothing to be found...
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
@Charles_Murison would you have a copy of the FAQ you are referring to, I don't think it's available online any more. We have a situation with a PM5560 meter where during the FW upgrade process it failed and the IP configuration is now IP Method: DHCP, IP Address: 255.255.255.255, Subnet:255.255.255.255, DNP3:Disbaled, MAC:FF:FF:FF:FF:FF:FF.
If the FAQ outlines how to re-establish a connection to the Meter to fix the issue that would be great.
Thanks,
Gavin
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
@Sparkey_90 , @Gavin_Bryson
https://www.se.com/ca/en/faqs/FA239202/
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Charles,
I have tried this potential resolution a few times but unfortunately, nothing has worked.
I have carried out further troubleshooting steps but nothing has worked. I have then gone back to the user manual for the PM5500 series and there is a piece in there regarding HW issues.
NOTE: A heartbeat LED that remains lit and does not blink (or flash) can indicate a
hardware problem
This was the case, as I could not detect any of the ethernet ports when connected, so it had to be a faulty piece of HW.