Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5350 error

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5350 error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Ken_Hsu
Ken_Hsu Mentor
Mentor

Posted: ‎2016-08-16 09:00 PM

0 Likes
6
2886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-16 09:00 PM

PM5350 error

Hello all

I have a customer using PM5350. The meter recently showed the "wrench" signal, and the hex error code is 0021.

The user manual states that the "wrench" signal indicates that the meter requires attention. However, I couldn't find any information on the error type.

Is there an error code document that can explain the meaning, and what actions to take?

Thank you ~~

Tags (3)
  • Tags:
  • error code
  • pm5350
  • wrench
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa52700
sesa52700 Leader
Leader

Posted: ‎2016-08-18 11:55 AM

0 Likes
4
2846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-18 11:55 AM

Hello Ken,

I checked with our technical team. The error code information is available in Register List (Address 20003 - user notes - bitmap format). . In this case, 0021 hex error code specifies, the measurement input signals are exceeding the direct input limits. Ensure that the connection is within the specified limits for the measurement signal. In the Troubleshooting section of the user guide, it recommends that if maintenance wrench is lit, you should contact tech support and give them the error code and any event messages.

Go to [Maint] > [Diag]. Event messages

display to indicate the reason the icon is

illuminated. Note these event messages and

call the Technical Support or contact your

local sales representative for assistance.

Regards,

Margie Myers

See Answer In Context

Reply
Replies 6
sesa52700
sesa52700 Leader
Leader

Posted: ‎2016-08-18 11:55 AM

0 Likes
4
2846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-18 11:55 AM

Hello Ken,

I checked with our technical team. The error code information is available in Register List (Address 20003 - user notes - bitmap format). . In this case, 0021 hex error code specifies, the measurement input signals are exceeding the direct input limits. Ensure that the connection is within the specified limits for the measurement signal. In the Troubleshooting section of the user guide, it recommends that if maintenance wrench is lit, you should contact tech support and give them the error code and any event messages.

Go to [Maint] > [Diag]. Event messages

display to indicate the reason the icon is

illuminated. Note these event messages and

call the Technical Support or contact your

local sales representative for assistance.

Regards,

Margie Myers

Reply
Ken_Hsu
Ken_Hsu Mentor
Mentor

Posted: ‎2016-08-18 07:43 PM

0 Likes
3
2846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-18 07:43 PM

Hi Margaret,

Thanks for your prompt reply.

I found the 20003 bitmap , as shown below. 0x21 translates to 0010 0001, which corresponds to Bit 01 Summary and Bit 06 Clipping Detected are turned on.  Is that correct?

0 = OK, 1 = Error Detected
Bit 01 = Summary
( on if any other bit is on - Maintenance Icon shown on HMI )
Bit 02 = RAM Failure
Bit 03 = NVRAM Failure
Bit 04 = RTC Failure
Bit 05 = Calibration Failure
Bit 06 = Clipping Detected
Bit 07 = Over-Running Energy Pulse Output
Bit 08-16 Not Used

I assume that "Clipping Detected" indicates that input measurements signals are exceeding the direct input limits. Does it differentiate between voltage and current?

In addition, is there a document that gives a more detailed explanation of the error codes?

Thank you~

Reply
sesa52700
sesa52700 Leader
Leader

Posted: ‎2016-08-19 08:12 AM

0 Likes
2
2846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-19 08:12 AM

Hi Ken, I'm checking again with the technical team for answers to your follow-up question, but perhaps a call to tech support would get you an answer quicker than in this Exchange. The good thing about calling tech support is that the question gets logged as an FAQ and the topic can be searched in the CCC (Customer Care Center) FAQ database. I've sent an email to the offer manager to let him know your request for better documentation on error messages.

Margie

Reply
Ken_Hsu
Ken_Hsu Mentor
Mentor

Posted: ‎2016-08-20 11:59 PM

0 Likes
1
2846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-20 11:59 PM

Noted.

Thank you Margie.

Your replies we're most helpful.

Ken

Reply
sesa52700
sesa52700 Leader
Leader

Posted: ‎2016-08-22 07:19 AM

0 Likes
0
2846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-22 07:19 AM

Ken, here is the response. He may contact you directly.

Hello Margie,

Please refer my replies in bold.

Hi Margaret,
Thanks for your prompt reply.
I found the 20003 bitmap , as shown below. 0x21 translates to 0010 0001, which corresponds to Bit 01 Summary and Bit 06 Clipping Detected are turned on.
Is that correct? - Yes, Correct.
0 = OK, 1 = Error Detected
Bit 01 = Summary
( on if any other bit is on - Maintenance Icon shown on HMI )
Bit 02 = RAM Failure
Bit 03 = NVRAM Failure
Bit 04 = RTC Failure
Bit 05 = Calibration Failure
Bit 06 = Clipping Detected
Bit 07 = Over-Running Energy Pulse Output
Bit 08-16 Not Used

I assume that "Clipping Detected" indicates that input measurements signals are exceeding the direct input limits.

Does it differentiate between voltage and current?  -There is no differentiation between voltage and current signals.

In addition, is there a document that gives a more detailed explanation of the error codes? 
- No.The customer should contact the Schneider tech support team as customer will not be able to act on it expect clipping and over run pulse output errors.

I will make a note about possibly improving our error code documentation. Thank you for the feedback!

Margie

Reply
odowaa
odowaa
Explorer

Posted: ‎2024-11-20 05:30 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-20 05:30 AM

I am using pm5350, I have a problem display,   my device backlight  is getting weak ,  if I change backlight timeout or even screen timeout  still my backlight is weak

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore