Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

PM5350 error

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5350 error
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
299
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
72
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Ken_Hsu
Commander Ken_Hsu Commander
Commander

Posted: ‎2016-08-16 09:00 PM

0 Likes
5
731
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-16 09:00 PM

PM5350 error

Hello all

I have a customer using PM5350. The meter recently showed the "wrench" signal, and the hex error code is 0021.

The user manual states that the "wrench" signal indicates that the meter requires attention. However, I couldn't find any information on the error type.

Is there an error code document that can explain the meaning, and what actions to take?

Thank you ~~

Tags (3)
  • Tags:
  • error code
  • pm5350
  • wrench
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa52700
sesa52700 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-08-18 11:55 AM

0 Likes
4
691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-18 11:55 AM

Hello Ken,

I checked with our technical team. The error code information is available in Register List (Address 20003 - user notes - bitmap format). . In this case, 0021 hex error code specifies, the measurement input signals are exceeding the direct input limits. Ensure that the connection is within the specified limits for the measurement signal. In the Troubleshooting section of the user guide, it recommends that if maintenance wrench is lit, you should contact tech support and give them the error code and any event messages.

Go to [Maint] > [Diag]. Event messages

display to indicate the reason the icon is

illuminated. Note these event messages and

call the Technical Support or contact your

local sales representative for assistance.

Regards,

Margie Myers

See Answer In Context

Reply
Replies 5
sesa52700
sesa52700 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-08-18 11:55 AM

0 Likes
4
692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-18 11:55 AM

Hello Ken,

I checked with our technical team. The error code information is available in Register List (Address 20003 - user notes - bitmap format). . In this case, 0021 hex error code specifies, the measurement input signals are exceeding the direct input limits. Ensure that the connection is within the specified limits for the measurement signal. In the Troubleshooting section of the user guide, it recommends that if maintenance wrench is lit, you should contact tech support and give them the error code and any event messages.

Go to [Maint] > [Diag]. Event messages

display to indicate the reason the icon is

illuminated. Note these event messages and

call the Technical Support or contact your

local sales representative for assistance.

Regards,

Margie Myers

Reply
Ken_Hsu
Commander Ken_Hsu Commander
Commander

Posted: ‎2016-08-18 07:43 PM

0 Likes
3
691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-18 07:43 PM

Hi Margaret,

Thanks for your prompt reply.

I found the 20003 bitmap , as shown below. 0x21 translates to 0010 0001, which corresponds to Bit 01 Summary and Bit 06 Clipping Detected are turned on.  Is that correct?

0 = OK, 1 = Error Detected
Bit 01 = Summary
( on if any other bit is on - Maintenance Icon shown on HMI )
Bit 02 = RAM Failure
Bit 03 = NVRAM Failure
Bit 04 = RTC Failure
Bit 05 = Calibration Failure
Bit 06 = Clipping Detected
Bit 07 = Over-Running Energy Pulse Output
Bit 08-16 Not Used

I assume that "Clipping Detected" indicates that input measurements signals are exceeding the direct input limits. Does it differentiate between voltage and current?

In addition, is there a document that gives a more detailed explanation of the error codes?

Thank you~

Reply
sesa52700
sesa52700 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-08-19 08:12 AM

0 Likes
2
691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-19 08:12 AM

Hi Ken, I'm checking again with the technical team for answers to your follow-up question, but perhaps a call to tech support would get you an answer quicker than in this Exchange. The good thing about calling tech support is that the question gets logged as an FAQ and the topic can be searched in the CCC (Customer Care Center) FAQ database. I've sent an email to the offer manager to let him know your request for better documentation on error messages.

Margie

Reply
Ken_Hsu
Commander Ken_Hsu Commander
Commander

Posted: ‎2016-08-20 11:59 PM

0 Likes
1
691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-20 11:59 PM

Noted.

Thank you Margie.

Your replies we're most helpful.

Ken

Reply
sesa52700
sesa52700 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-08-22 07:19 AM

0 Likes
0
691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-22 07:19 AM

Ken, here is the response. He may contact you directly.

Hello Margie,

Please refer my replies in bold.

Hi Margaret,
Thanks for your prompt reply.
I found the 20003 bitmap , as shown below. 0x21 translates to 0010 0001, which corresponds to Bit 01 Summary and Bit 06 Clipping Detected are turned on.
Is that correct? - Yes, Correct.
0 = OK, 1 = Error Detected
Bit 01 = Summary
( on if any other bit is on - Maintenance Icon shown on HMI )
Bit 02 = RAM Failure
Bit 03 = NVRAM Failure
Bit 04 = RTC Failure
Bit 05 = Calibration Failure
Bit 06 = Clipping Detected
Bit 07 = Over-Running Energy Pulse Output
Bit 08-16 Not Used

I assume that "Clipping Detected" indicates that input measurements signals are exceeding the direct input limits.

Does it differentiate between voltage and current?  -There is no differentiation between voltage and current signals.

In addition, is there a document that gives a more detailed explanation of the error codes? 
- No.The customer should contact the Schneider tech support team as customer will not be able to act on it expect clipping and over run pulse output errors.

I will make a note about possibly improving our error code documentation. Thank you for the feedback!

Margie

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc