Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

PM5320 no Ping an no changes in ION Setup possible

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5320 no Ping an no changes in ION Setup possible
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
299
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
72
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Sven_Ortmann
Commander Sven_Ortmann Commander
Commander

Posted: ‎2018-08-30 05:02 AM

0 Likes
4
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-30 05:02 AM

PM5320 no Ping an no changes in ION Setup possible

Hello,

customer does have many PM5320 Meters. For the network team it is not possible to ping the devices.

PROBLEM 1: static ip address will only be applied after a power off - power on

PROBLEM 2: It is not possible to open ftp://IPAdress  or http://IPAdress

PROBLEM 3: Windows Explorer shows the device at network but the information is strange:

PROBLEM 4: in ION Setup it is not possible to set the ip adress because this point is not visible.

And it is not possible to change the serial parameter from odd to even

With this barcode you can see further informations:

this is the serial number of one of these devices:

firmware seems to be newest one:

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Commander Ramasamy_N Commander
Commander

Posted: ‎2018-08-31 01:39 AM

1 Like
0
636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-31 01:39 AM

Hello Sven,

Please refer my comments in green,

PROBLEM 1: static ip address will only be applied after a power off - power on

The static IP address will be stored once after configure the IP,sub net,Gateway. It does not required to power off. It may take some time (1 to 2 minutes) to stored the configuration depending on the network traffic. 

-> we were waiting more than 2 minutes but it was not possible to connect, after a power off and on it works with several devices.

-->Please check and update this condition in one meter with a standalone system in same IP settings

PROBLEM 2: It is not possible to open ftp://IPAdress  or http://IPAdress

PM5320 does not support HTTP or FTP protocol

-> how to upgrade firmware for PM5320 without FTP?    

-->PM53xx series meters can be upgrade the firmware using DLF3000 tool.

PROBLEM 4: in ION Setup it is not possible to set the ip adress because this point is not visible.

And it is not possible to change the serial parameter from odd to even

PM5340 com link must be configured as Ethernet devices in ION setup and enter the IP address of device in insert device -> new device page. Serial parameters are applicable only for Serial RS485 devices.

-> so if we need to implement to PME Software, the devices are always IP Adress and ID 255 ?

--> Yes.

Regards,

Ramasamy N

See Answer In Context

Reply
Replies 4
Ramasamy_N
Commander Ramasamy_N Commander
Commander

Posted: ‎2018-08-30 08:33 PM

1 Like
2
636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-30 08:33 PM

Hello Sven,

Please refer my comments below,

PROBLEM 1: static ip address will only be applied after a power off - power on

The static IP address will be stored once after configure the IP,sub net,Gateway. It does not required to power off. It may take some time (1 to 2 minutes) to stored the configuration depending on the network traffic.  

PROBLEM 2: It is not possible to open ftp://IPAdress  or http://IPAdress

PM5320 does not support HTTP or FTP protocol

PROBLEM 3: Windows Explorer shows the device at network but the information is strange:

This is know error ans escalated to product owner for fixing in the upcoming release.

PROBLEM 4: in ION Setup it is not possible to set the ip adress because this point is not visible.

And it is not possible to change the serial parameter from odd to even

PM5340 com link must be configured as Ethernet devices in ION setup and enter the IP address of device in insert device -> new device page. Serial parameters are applicable only for Serial RS485 devices.

Regards,

Ramasamy N

Reply
Sven_Ortmann
Commander Sven_Ortmann Commander
Commander

Posted: ‎2018-08-31 12:22 AM

0 Likes
1
636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-31 12:22 AM

Hello Ramasamy N​,

thanky for your comments:

se my new comments

PROBLEM 1: static ip address will only be applied after a power off - power on

The static IP address will be stored once after configure the IP,sub net,Gateway. It does not required to power off. It may take some time (1 to 2 minutes) to stored the configuration depending on the network traffic.  

-> we were waiting more than 2 minutes but it was not possible to connect, after a power off and on it works with several devices.

PROBLEM 2: It is not possible to open ftp://IPAdress  or http://IPAdress

PM5320 does not support HTTP or FTP protocol

-> how to upgrade firmware for PM5320 without FTP?

PROBLEM 3: Windows Explorer shows the device at network but the information is strange:

This is know error ans escalated to product owner for fixing in the upcoming release.

-> thanks

PROBLEM 4: in ION Setup it is not possible to set the ip adress because this point is not visible.

And it is not possible to change the serial parameter from odd to even

PM5340 com link must be configured as Ethernet devices in ION setup and enter the IP address of device in insert device -> new device page. Serial parameters are applicable only for Serial RS485 devices.

-> so if we need to implement to PME Software, the devices are always IP Adress and ID 255 ? 

Regards,

Sven

Reply
Ramasamy_N
Commander Ramasamy_N Commander
Commander

Posted: ‎2018-08-31 01:39 AM

1 Like
0
637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-31 01:39 AM

Hello Sven,

Please refer my comments in green,

PROBLEM 1: static ip address will only be applied after a power off - power on

The static IP address will be stored once after configure the IP,sub net,Gateway. It does not required to power off. It may take some time (1 to 2 minutes) to stored the configuration depending on the network traffic. 

-> we were waiting more than 2 minutes but it was not possible to connect, after a power off and on it works with several devices.

-->Please check and update this condition in one meter with a standalone system in same IP settings

PROBLEM 2: It is not possible to open ftp://IPAdress  or http://IPAdress

PM5320 does not support HTTP or FTP protocol

-> how to upgrade firmware for PM5320 without FTP?    

-->PM53xx series meters can be upgrade the firmware using DLF3000 tool.

PROBLEM 4: in ION Setup it is not possible to set the ip adress because this point is not visible.

And it is not possible to change the serial parameter from odd to even

PM5340 com link must be configured as Ethernet devices in ION setup and enter the IP address of device in insert device -> new device page. Serial parameters are applicable only for Serial RS485 devices.

-> so if we need to implement to PME Software, the devices are always IP Adress and ID 255 ?

--> Yes.

Regards,

Ramasamy N

Reply
Robert_Lee
Captain Robert_Lee Captain
Captain

Posted: ‎2018-08-31 07:43 PM

0 Likes
0
636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-31 07:43 PM

ION Setup is unable to program IP information as it is not readily available via Modbus.

As for the "Unable to gain device setup access" error dialog, this likely indicates someone has setup access via the front panel (or thru communications by obtaining the setup semaphore).

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc