Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5320 no Ping an no changes in ION Setup possible

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5320 no Ping an no changes in ION Setup possible
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
195
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Sven_Ortmann
Sven_Ortmann Leader
Leader

Posted: ‎2018-08-30 05:02 AM

0 Likes
4
2643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-30 05:02 AM

PM5320 no Ping an no changes in ION Setup possible

Hello,

customer does have many PM5320 Meters. For the network team it is not possible to ping the devices.

PROBLEM 1: static ip address will only be applied after a power off - power on

PROBLEM 2: It is not possible to open ftp://IPAdress  or http://IPAdress

PROBLEM 3: Windows Explorer shows the device at network but the information is strange:

PROBLEM 4: in ION Setup it is not possible to set the ip adress because this point is not visible.

And it is not possible to change the serial parameter from odd to even

With this barcode you can see further informations:

this is the serial number of one of these devices:

firmware seems to be newest one:

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2018-08-31 01:39 AM

1 Like
0
2610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-31 01:39 AM

Hello Sven,

Please refer my comments in green,

PROBLEM 1: static ip address will only be applied after a power off - power on

The static IP address will be stored once after configure the IP,sub net,Gateway. It does not required to power off. It may take some time (1 to 2 minutes) to stored the configuration depending on the network traffic. 

-> we were waiting more than 2 minutes but it was not possible to connect, after a power off and on it works with several devices.

-->Please check and update this condition in one meter with a standalone system in same IP settings

PROBLEM 2: It is not possible to open ftp://IPAdress  or http://IPAdress

PM5320 does not support HTTP or FTP protocol

-> how to upgrade firmware for PM5320 without FTP?    

-->PM53xx series meters can be upgrade the firmware using DLF3000 tool.

PROBLEM 4: in ION Setup it is not possible to set the ip adress because this point is not visible.

And it is not possible to change the serial parameter from odd to even

PM5340 com link must be configured as Ethernet devices in ION setup and enter the IP address of device in insert device -> new device page. Serial parameters are applicable only for Serial RS485 devices.

-> so if we need to implement to PME Software, the devices are always IP Adress and ID 255 ?

--> Yes.

Regards,

Ramasamy N

See Answer In Context

Reply
Replies 4
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2018-08-30 08:33 PM

1 Like
2
2610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-30 08:33 PM

Hello Sven,

Please refer my comments below,

PROBLEM 1: static ip address will only be applied after a power off - power on

The static IP address will be stored once after configure the IP,sub net,Gateway. It does not required to power off. It may take some time (1 to 2 minutes) to stored the configuration depending on the network traffic.  

PROBLEM 2: It is not possible to open ftp://IPAdress  or http://IPAdress

PM5320 does not support HTTP or FTP protocol

PROBLEM 3: Windows Explorer shows the device at network but the information is strange:

This is know error ans escalated to product owner for fixing in the upcoming release.

PROBLEM 4: in ION Setup it is not possible to set the ip adress because this point is not visible.

And it is not possible to change the serial parameter from odd to even

PM5340 com link must be configured as Ethernet devices in ION setup and enter the IP address of device in insert device -> new device page. Serial parameters are applicable only for Serial RS485 devices.

Regards,

Ramasamy N

Reply
Sven_Ortmann
Sven_Ortmann Leader
Leader

Posted: ‎2018-08-31 12:22 AM

0 Likes
1
2610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-31 12:22 AM

Hello Ramasamy N​,

thanky for your comments:

se my new comments

PROBLEM 1: static ip address will only be applied after a power off - power on

The static IP address will be stored once after configure the IP,sub net,Gateway. It does not required to power off. It may take some time (1 to 2 minutes) to stored the configuration depending on the network traffic.  

-> we were waiting more than 2 minutes but it was not possible to connect, after a power off and on it works with several devices.

PROBLEM 2: It is not possible to open ftp://IPAdress  or http://IPAdress

PM5320 does not support HTTP or FTP protocol

-> how to upgrade firmware for PM5320 without FTP?

PROBLEM 3: Windows Explorer shows the device at network but the information is strange:

This is know error ans escalated to product owner for fixing in the upcoming release.

-> thanks

PROBLEM 4: in ION Setup it is not possible to set the ip adress because this point is not visible.

And it is not possible to change the serial parameter from odd to even

PM5340 com link must be configured as Ethernet devices in ION setup and enter the IP address of device in insert device -> new device page. Serial parameters are applicable only for Serial RS485 devices.

-> so if we need to implement to PME Software, the devices are always IP Adress and ID 255 ? 

Regards,

Sven

Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2018-08-31 01:39 AM

1 Like
0
2611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-31 01:39 AM

Hello Sven,

Please refer my comments in green,

PROBLEM 1: static ip address will only be applied after a power off - power on

The static IP address will be stored once after configure the IP,sub net,Gateway. It does not required to power off. It may take some time (1 to 2 minutes) to stored the configuration depending on the network traffic. 

-> we were waiting more than 2 minutes but it was not possible to connect, after a power off and on it works with several devices.

-->Please check and update this condition in one meter with a standalone system in same IP settings

PROBLEM 2: It is not possible to open ftp://IPAdress  or http://IPAdress

PM5320 does not support HTTP or FTP protocol

-> how to upgrade firmware for PM5320 without FTP?    

-->PM53xx series meters can be upgrade the firmware using DLF3000 tool.

PROBLEM 4: in ION Setup it is not possible to set the ip adress because this point is not visible.

And it is not possible to change the serial parameter from odd to even

PM5340 com link must be configured as Ethernet devices in ION setup and enter the IP address of device in insert device -> new device page. Serial parameters are applicable only for Serial RS485 devices.

-> so if we need to implement to PME Software, the devices are always IP Adress and ID 255 ?

--> Yes.

Regards,

Ramasamy N

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2018-08-31 07:43 PM

0 Likes
0
2610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-31 07:43 PM

ION Setup is unable to program IP information as it is not readily available via Modbus.

As for the "Unable to gain device setup access" error dialog, this likely indicates someone has setup access via the front panel (or thru communications by obtaining the setup semaphore).

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.