PM5110 display value

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5110 display value
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa191869
sesa191869 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-09-14 06:34 PM

0 Likes
7
1755
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-09-14 06:34 PM

PM5110 display value

Hello,

As far as I know PM5110 does not measure ground current. Then what does Ig mean in PM5110 display?

Look forward to your help. Thanks.

rtaImage.jpg

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2017-09-15 02:10 AM

0 Likes
0
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-09-15 02:10 AM

Hi Soo-Yul,

The Ground current (Ig) and Neutral current (In) will be displayed based on the wire system was selected in PM51/5300 series meters. 3PH3W system the Neutral current will not be applicable, so the meter is displayed Ground current (Ig).

The Ground current calculation method of PM5110 and PM5560 are same.

Regards,

Ramasamy.N

See Answer In Context

Reply
Replies 7
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2017-09-14 09:50 PM

0 Likes
2
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-09-14 09:50 PM

Hello Soo-Yul,

The ground current value displayed in PM5110 is calculated value using vector sum formula.

However the Ig value displayed in this meter is wrong, I request you to check the phase angle between all three phase inputs.

It should be 120 degree between any two phases.

Regards,

Ramasamy.N

Reply
sesa191869
sesa191869 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-09-14 10:24 PM

0 Likes
1
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-09-14 10:24 PM

Dear Ramasamy,

Thank you for your reply. For your information, it is 3 phase 3 wire system using 3 CT. Why do we still need to show Ig value?

By the way, I thought only PM556X can measure ground current, isn't it?

Regards,

Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2017-09-15 02:10 AM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-09-15 02:10 AM

Hi Soo-Yul,

The Ground current (Ig) and Neutral current (In) will be displayed based on the wire system was selected in PM51/5300 series meters. 3PH3W system the Neutral current will not be applicable, so the meter is displayed Ground current (Ig).

The Ground current calculation method of PM5110 and PM5560 are same.

Regards,

Ramasamy.N

Reply
Anonymous user
Not applicable

Posted: ‎2018-08-20 02:40 AM

0 Likes
3
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-20 02:40 AM

Hi Everyone,

I have same problem with my new PM5350, replacing analog kwhmeter on old switchgear, others reading is Ok, except Ig is wrong. Is there something wrong with wiring? or something else?

FYI, the meters installed at one switchgear, thereis old/existing 1 PM5350 with zero (0) Ig reading, now i install 15 new PM5350 and all Ig reading is wrong

PM5350 IG.jpg

pm5350 ig wrong.jpeg

Please help if you have same problem and solved.

Regards,

Guntur

Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2018-08-20 04:10 AM

0 Likes
2
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-20 04:10 AM

Hello Gutur,

Ig is a calculated value in PM5350 series meters. Can you please check the phase angle of new PM5350? It looks 2 phases are in same angle and it must be 120 degree between other phases.

Regards,

Ramasamy N

Reply
Anonymous user
Not applicable

Posted: ‎2018-08-20 07:46 PM

0 Likes
1
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-20 07:46 PM

hi Ramasamy,

what can i do if phases in same angle? what causes that? i dont have any idea about it. can i fix it with swap voltage terminal, R or S or T?

thankyou for response

regards,

Guntur

Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2018-08-21 02:47 AM

0 Likes
0
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-21 02:47 AM

Hi Guntur,

Please check the CT connection in the meter, it should match with the wiring diagram specified in the installation guide.

The Ig value displayed as sum of 2 phase current, if the phase angle of any 2 phases are same. I suggest you check current inputs again.

Regards,

Ramasamy N

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of