Hi guys!
We have 2 distinct datasheets of the ION8650 and we note that there is a difference in the item "Input-current characterístics".
Technical Datasheet - 2011

ION8650 Technical Datasheet - Web Version - 2017

Has this changed or 1 document is wrong?
Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Hi
I dug into this a bit more and it appears as if data has been a bit mixed in the 2017 Technical Datasheet. The 2011 datasheet is correct for the per phase burden for the CT's. However, the information given in the 2017 is relevant to the power-supply burden for Standard 3-phase power-supply, blade powered (The line below it). I will take this up to have it corrected in the next edition. My apologies for the mix-up.
I hope this clears it up. If you have more questions, please let me know!
Regards,
Sanjeet
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi
I dug into this a bit more and it appears as if data has been a bit mixed in the 2017 Technical Datasheet. The 2011 datasheet is correct for the per phase burden for the CT's. However, the information given in the 2017 is relevant to the power-supply burden for Standard 3-phase power-supply, blade powered (The line below it). I will take this up to have it corrected in the next edition. My apologies for the mix-up.
I hope this clears it up. If you have more questions, please let me know!
Regards,
Sanjeet
Posted: 2018-08-16 11:10 AM . Last Modified: 2025-05-13 10:44 PM
Link copied. Please paste this link to share this article on your social media post.
Hi
Thanks for your reply!