In case of PM5563 and also PM8000 does the demand shown on the meter display switch between kW, MW, GW ? If so, what is the boundary at which this switching happens?
Does this affect the numbers that are read through communications?
Is it possible to "lock" the display to only one of kW or MW or GW and not have it scale?
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Thank you Charles_M for the answer regarding the PM8000 series. Below is how PM55000 series meters work:
The units for Energy values change automatically from Wh to kWh, kWh to MWh, MWh to GWh, GWh to TWh, TWh to PWh, we cannot restrict or limit this change in this meter series.
This is how energy readings on PM5500 display rollover and change units:
And once value reaches 9223.3 PWh , energy value rollovers and start accumulating again automatically.
Link copied. Please paste this link to share this article on your social media post.
Have you looked at https://www.schneider-electric.com/en/faqs/index?page=content&id=FA203886 for the PM8000. For the PM5563 I am not sure.
Link copied. Please paste this link to share this article on your social media post.
Thank you Charles_M for the answer regarding the PM8000 series. Below is how PM55000 series meters work:
The units for Energy values change automatically from Wh to kWh, kWh to MWh, MWh to GWh, GWh to TWh, TWh to PWh, we cannot restrict or limit this change in this meter series.
This is how energy readings on PM5500 display rollover and change units:
And once value reaches 9223.3 PWh , energy value rollovers and start accumulating again automatically.