Do we need to remove all inputs from PM series meters (such as Voltage & Current Inputs) while doing a firmware upgradation? I will very thankful for any guidance in this matter. 🙂
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Asif_Khan ,
No the voltage and current connections do not have to be removed to upgrade a meter. I would recommend disconnecting any software that may be trying to talk to the meter.
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Asif_Khan ,
No the voltage and current connections do not have to be removed to upgrade a meter. I would recommend disconnecting any software that may be trying to talk to the meter.
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @Asif_Khan
Also, if meter has any IO connections like Digital output, their state during a firmware upgrade may change.
Best Regards,
-Mehran
L3 Expert Technical Support Specialist