Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM3255 Multi tariff settings

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM3255 Multi tariff settings
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
203
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Twanda
Twanda
Explorer

Posted: ‎2023-03-31 07:43 AM

0 Likes
2
2235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-31 07:43 AM

PM3255 Multi tariff settings

  •  

Hello Everybody 

I recently bought PM3255s and I'm having challenges setting the multi tariff schedules via the internal clock option. Could you please, kindly, assist I have a client at my neck
[3/31, 4:23 PM] rtmukwasi: When I go to week day scheduling I notice 4 segments appear each segment starts of with *N/A* what does this mean? Scrolling the segment via the up & down button the segment goes to *N/A*, *T1*, *T2*, *T3*, *T4* with each tariff section having a start time

How do I program the *peak*, *off peak*, *Standard* rates also considering that a day has 2 peak and 2 standard schedules and 1 off peak schedule

How do I also incorporate holiday tariffs which may occur during the week day?

For weekends: Saturday & Sunday has different reschedules. How do I program them apart.

Lastly,, is it possible to download weekly or monthly energy logs as excel files so that I can use other software to do analysis and cost allocation

Labels
  • Labels:
  • PM3000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2023-04-04 10:24 AM

1 Like
0
2195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-04 10:24 AM

Are you sure the devices are PM3255s?  Those models do not mention having any ability to do on-board Time of Use.  From your description of T1 thru T4, that sounds more like EM2x55 than the PM3255.

For the EM2x55, there is a "Time of Use" configuration option via ION Setup which allows you to program the Daily/Weekly/Monthly Rates, plus Fixed and Variable Holidays.

Using ION Setup you can view the Flex Log but presently there is no export option to Excel directly (a File Save option could be added to the file viewer but this would be a manual operation and requires editing the default file).  Another option is you could cut & paste from the ION Setup viewer directly into Excel.  PME might be a better solution if you want to have the flex log downloaded automatically.

See Answer In Context

Reply
Replies 2
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2023-04-04 10:24 AM

1 Like
0
2196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-04 10:24 AM

Are you sure the devices are PM3255s?  Those models do not mention having any ability to do on-board Time of Use.  From your description of T1 thru T4, that sounds more like EM2x55 than the PM3255.

For the EM2x55, there is a "Time of Use" configuration option via ION Setup which allows you to program the Daily/Weekly/Monthly Rates, plus Fixed and Variable Holidays.

Using ION Setup you can view the Flex Log but presently there is no export option to Excel directly (a File Save option could be added to the file viewer but this would be a manual operation and requires editing the default file).  Another option is you could cut & paste from the ION Setup viewer directly into Excel.  PME might be a better solution if you want to have the flex log downloaded automatically.

Reply
Twanda
Twanda
Explorer

Posted: ‎2023-04-04 10:19 PM

0 Likes
0
2183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-04 10:19 PM

Thank you for the response.

 

Yes the PM3255 has the multi tariff on board setup. There are 4 time segments which can be assigned tariff 1 to tariff 4. I later figured out how to set it up. 

 

The big draw back though is that there is no provision for holidays and the weekend tariff (Saturday & Sunday) does not take into consideration that Saturday and Sunday have different tariffs they are just treated as having one tariff. This is why I need to just have a csv file that I can use on more flexible software.

 

Thanks.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore