Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Needs PM600 meter support in ION Setup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Needs PM600 meter support in ION Setup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Yu_Diao
Yu_Diao Leader
Leader

Posted: ‎2013-04-04 12:30 AM . Last Modified: ‎2020-04-22 01:47 AM

1 Like
13
4523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-04-04 12:30 AM

Needs PM600 meter support in ION Setup

As PM6 series meter becomes native device in SPM, we need a tool to config the on-board log of PM650, since that is where SPM gets all the metering data. Right now, only SMS or PMCU, which we try to get ride of, can do this.

 

Understand that PM6s have been obsoleted for a long long time. Even I was surprised about their large existence when I found about half of 200+ meters system were PM6 (mainly PM650) in a SMS2SPM job I recently worked on. Just like the new native PM6 driver in SPM, I believe it is worth being supported by ION Setup either.

 

Regards,

Labels
  • Labels:
  • ION Setup
Tags (2)
  • Tags:
  • ion_setup
  • pm6
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2014-02-28 11:16 AM

1 Like
10
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-28 11:16 AM

I've been trying to add old legacy support for these older products whenever I have a few days available but its very slow going.  With that said, the latest version does have most of the configuration screens available and the device is available in the supported device list.

Download the latest version and give it a try and if you find any issues let me know and I'll take a look at it if I get some available time.

See Answer In Context

Reply
Replies 13
Yu_Diao
Yu_Diao Leader
Leader

Posted: ‎2013-08-08 11:27 PM

0 Likes
0
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-08-08 11:27 PM

Robert, wonder if there are any plans in place to support PM600 meters at all?

is.gdCrunchbase: is.gd is a company (Consumer Web), acquired by Memset. →

Reply
Yu_Diao
Yu_Diao Leader
Leader

Posted: ‎2014-02-25 04:51 PM

1 Like
11
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-25 04:51 PM

After 7 months, We are still running into the same issue when trying to config PM600 especially PM650 on-site. We have fewer and fewer running SMS system, and the PMCU is a pain to even install. , is there any plan to add the PM600 support into ION Setup?

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2014-02-28 11:16 AM

1 Like
10
4326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-28 11:16 AM

I've been trying to add old legacy support for these older products whenever I have a few days available but its very slow going.  With that said, the latest version does have most of the configuration screens available and the device is available in the supported device list.

Download the latest version and give it a try and if you find any issues let me know and I'll take a look at it if I get some available time.

Reply
Yu_Diao
Yu_Diao Leader
Leader

Posted: ‎2014-03-05 03:45 PM

0 Likes
9
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-05 03:45 PM

Robert,

I tried the newest release V3.0.14052.02 on the FTP site, and it works with PM6. Coudl we go one step ahead to add the function to config the "on-board alarm" for PM650?

Also, the on-board log is only available to PM650, should we remove it from "Default" display template (everything except PM650)?


Regards,

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2014-03-05 04:04 PM

1 Like
8
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-05 04:04 PM

The "Default" folder is the one which is set by ION Setup initially and is only used when it can't tell what type of device it is.  If for example a newer model came out (ex. PM680 with more features), then the software defaults to show the maximum available features (but just won't support the newer features).  This is why all the "Default" folders contain the identical device setup files as the highest model (assuming any new models which come along will have more features than less).

The Default folder shouldn't be used unless ION Setup isn't properly determining the type of device its communicating to (when it is presently set to Default, it will always try to override this setting by talking to the device and seeing if it matches what it think it should be set to).  If its set to Default and the device is a PM620 actually, then it should switch to the PM620 folder automatically every time (if not, then I'm not determining the PM620 correctly or its sending something back I'm not expecting).  In this case, you should let me know the details.

I'll see about adding the On-Board Alarm configuration but as I said before its very slow going as everything has to be reverse engineered, coded and go through some preliminary testing (and I have no means to do any real extensive testing).

Reply
Yu_Diao
Yu_Diao Leader
Leader

Posted: ‎2014-03-05 04:30 PM

0 Likes
0
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-05 04:30 PM

Robert,

Thanks for the elaboration, it makes sense now. In my case, I believe it must be related to the installation/upgrade. On the target machine, there were a old copy of ION Setup V3, and I just did an "upgrade" using V3.0.14052.02 installer. The result: some templates did not created. For example, under "CM2000" folder, I only got "CM2450" and "Default", and I had to create copies of "CM2450" and rename them to "CM2150", "CM2250"... to accommodate all CM2 meters on the site.

I just tried again on a VM, where I uninstalled the old ION Setup first, and did a fresh new installation, this time everything showed up correctly including all CM2s and PM6s. I don't have access to the target machine now, when I do I will definitely check out the behavior for PM6 again.

Regards,

Reply
ganesh_azzo_com
ganesh_azzo_com
Troubleshooter

Posted: ‎2014-06-30 12:17 AM

0 Likes
6
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-06-30 12:17 AM

Hi with a latest ION setup version 3.0.14174.02 , i am not able to access the PM650 , i tried with few lower version still failed to access the page. When i double click on the meter nothing come's up and in the left hand bottom corner it show's only as "ION Setup"

4061

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2014-06-30 08:57 AM

0 Likes
5
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-06-30 08:57 AM

Hi Ganesh,

I have an almost identical PM650 in my office connected to my 7650 Modbus Gateway (a little older Display firmware but otherwise almost identical) and have no issues communicating to the meter.

40644065

Are you sure you have the proper device type defined and what selection is selected beneath the Display tab on the device properties?

40664067

Reply
ganesh_azzo_com
ganesh_azzo_com
Troubleshooter

Posted: ‎2014-06-30 05:37 PM

0 Likes
4
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-06-30 05:37 PM

Hi , , what i found is when i upgrade the the ION setup from Lower version to latest version it doesn't seem to be happy . I had to uninstall and install the latest version and restart the server to make it work.  But now it show's up Download incomplete on the bottom left corner. And i am able not to send anything to meter

4062

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2014-07-04 09:44 AM

2 Likes
3
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-04 09:44 AM

I've uploaded a new version (V3.0.14185.01) on Box which should fix the PM6xx data log setup issues. I've also added Meter Configuration report for the PM6xx as well.

Reply
ganesh_azzo_com
ganesh_azzo_com
Troubleshooter

Posted: ‎2014-07-06 09:16 PM

0 Likes
2
4323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-06 09:16 PM

Hi , , I tried the latest version , but there are different set of issues now , Once the data logs are selected in ION set up and written into the meter . It doesn't seems to write in the meter and throw's up Dialogue "Unable to find 40003 in register Map. I have sent an email with video Link . Thanks for your support.

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2014-07-11 11:42 AM

2 Likes
1
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-11 11:42 AM

New version now available (3.0.14192.02) on Box which which has added a new set of registers for both Alarm/Data Log which will show Log Memory used (by that log) and Available Memory remaining (unused).  This will also limit what will be allowed to be set for the depth of the log and the # of parameters for data log #1 (which will only indicate that you have exceeded the allowable memory).  You may need to do trial & error to figure out how many registers each combination of parameters uses to maximize allocation (you will have to reduce depth/parameters in order to allow changes).

4166

Reply
JamesAZZO
JamesAZZO
Leader

Posted: ‎2014-07-11 07:22 PM

0 Likes
0
4321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-11 07:22 PM

Rob Lee - comes through with the goods! Thanks mate!!!

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore