IEM3255 com.protection takes effect also for Reset Partial counter over Modbus?
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2014-04-0903:26 AM
IEM3255 com.protection takes effect also for Reset Partial counter over Modbus?
Hallo,
Customer have 2 meters IEM3255 (different Firmware 1.03 and 1.08), he tries to reset the Partial counter over Modbus (function 2020)
This function is working with firmware 1.0.3 without poblem but with the meter firmware 1.0.8 not.
someone told me to check "com.protection", but it was enabled on both meters, and i does'nt found any information if this parameter taking effect for Reset or only lock change configurations.
Link copied. Please paste this link to share this article on your social media post.
2014-07-1402:19 PM
I realize this is an older post but I'll answer for future reference. I checked with the development team, and it seems like Com. Protection was extended to cover function 2020 in firmware v1.0.600, so that would account for the difference you're seeing.