Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84398members
353586posts

NRC12 Parity

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
sesa6201_bridge
Crewman Crewman
Crewman
0 Likes
1
217

NRC12 Parity

We are using Varlogic NRC12 model with MCU converter for the Modbus communication. Setting of Parity is EVEN it is fixed and we can’t change.

SCADA (Seimens) supplier  required Parity is NONE. can you please advice the solution.


Accepted Solutions
NeiB
Ensign Ensign
Ensign

Re: NRC12 Parity

Hi Basim, hope you are doing well.

Unfortunately there is no way to have parity NONE or ODD at the NRC12. Now with the new VarPlus Logic this option is available. This is the answer of our Expert Support in France for the same question in a bfo case.

Cheers!!

Neide - TSC SouthAmerica

See Answer In Context

1 Reply 1
NeiB
Ensign Ensign
Ensign

Re: NRC12 Parity

Hi Basim, hope you are doing well.

Unfortunately there is no way to have parity NONE or ODD at the NRC12. Now with the new VarPlus Logic this option is available. This is the answer of our Expert Support in France for the same question in a bfo case.

Cheers!!

Neide - TSC SouthAmerica