NERC Standard MOD-026-1 / MOD-027-1 compliance for ION 7650 & ION 7400 meters

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • NERC Standard MOD-026-1 / MOD-027-1 compliance for ION 7650 & ION 7400 meters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Hady_Kholeif
Ensign Hady_Kholeif Ensign
Ensign

Posted: ‎2019-04-02 02:34 AM . Last Modified: ‎2019-04-05 01:59 PM

0 Likes
4
3675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-02 02:34 AM

NERC Standard MOD-026-1 / MOD-027-1 compliance for ION 7650 & ION 7400 meters

Hello,

 

I am working with BC Hydro to determine whether we can use an ION 7650 meter or an ION 7400 meter to show compliance for both NERC MOD-026-1 and MOD-027-1 standards.

 

MOD-026-1 - To verify that the generator excitation control system or plant volt/var control function model (including the power system stabilizer model and the impedance compensator model) and the model parameters used in dynamic simulations accurately represent the generator excitation control system or plant volt/var control function behaviour when assessing Bulk Electric System (BES) reliability.

 

MOD-027-1  - To verify that the turbine/governor and load control or active/frequency control model and the model parameters used in dynamic simulations that assess BES reliability, accurately represent the generator unit real power response to system frequency variations.

 

Specifically for the MOD-027-1 standard, in order for the meter to conform to NERC's requirements: the customer would like to be able to log the following data:

 

- Real Power (RMS)

- Reactive Power (RMS)

- Voltage L-L (RMS)

- Frequency

 

for a period of 2 minutes at a 20Hz sampling rate (Output recording rate of monitoried parameters of at least 20 times/second?) when triggered by a (Setpoint Module) for a frequency deviation of (e.g. +/- 0.2 Hz).

 

2019-04-01 18_06_47-Photos.png

 

I understand that the ION 8650 meter is the only NERC compliant meter at this time according to:

https://www.schneider-electric.com/en/faqs/FA319340/

 

I would like to explore the possibility of showing NERC compliance via one of the following two methods:

 

1. High-speed Logging (1/2 cycle ~ 8.33 ms) update rate. I believe this would meet the 20Hz sampling rate requirement (which would be 1000ms / 20Hz = 50ms). I would need to find a method to trigger the data recorder module once every  3 cycles (or 50ms). Possibly a counter module in conjunction with a one-shot timer module may help achieve this.

 

2. Waveform Capture. The plan here is to use cascaded waveforms, however, this would not be possible for a period of 2 min, Looking at the 'extended waveform capture' feature in the ION9000,I understand that it allows up to 30 cycles of pre-event waveform records at 1024 (max sampling rate) and 30 cycles of event data. This waveform recorder can then be retriggered to extend the waveform for up to 180 cycles. It can then re-trigger that capture for a user defined number of captures limited by memory. Has this feature been ported to the PM8000/ION7400 platform?

 

Given the above, is it possible for either of the ION 7650 or ION 7400 meters to accomplish this? What are your recommendations?

 

Attached are both MOD-026-1 / MOD-027-1 NERC standards for your reference.

 

Regards,

Hady

Attachments
Tags (4)
  • Tags:
  • 7400
  • 7650
  • ion
  • NERC
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-04-02 05:22 PM

0 Likes
2
3665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-02 05:22 PM

Hey Hadi,

 

Couple points:

The KB should be updated to state NERC CIP which is related to cybersecurity. NERC MOD is something different.

 

For the logging, I am having trouble finding the specs/measurements from the attached pdf. When I asked hardware there were a couple of red flags

Real power is not true RMS, reactive power has a number of different methods to calculate, each methd has pros and cons and can result in different outputs.

 

Have you looked into the burst Data recording of the ION7400 meters?

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 4
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-04-02 09:34 AM

0 Likes
0
3672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-02 09:34 AM

@sesa56307_bridg  

 

Any thoughts?

L4 Prime for Advanced metering and Utilities
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-04-02 05:22 PM

0 Likes
2
3666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-02 05:22 PM

Hey Hadi,

 

Couple points:

The KB should be updated to state NERC CIP which is related to cybersecurity. NERC MOD is something different.

 

For the logging, I am having trouble finding the specs/measurements from the attached pdf. When I asked hardware there were a couple of red flags

Real power is not true RMS, reactive power has a number of different methods to calculate, each methd has pros and cons and can result in different outputs.

 

Have you looked into the burst Data recording of the ION7400 meters?

L4 Prime for Advanced metering and Utilities
Reply
Hady_Kholeif
Ensign Hady_Kholeif Ensign
Ensign

Posted: ‎2019-04-02 06:05 PM

0 Likes
1
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-02 06:05 PM

Hi Charles,

 

Thanks for your response. What methods are available for calculation of P and Q? Shall I use the standard 3-phase power formulas or do you have another recommeneded method?

 

Thanks,

Hady

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-04-03 08:23 AM

0 Likes
0
3656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-03 08:23 AM

Using the phrase RMS for real power is not mathamaticaly sound. I would still use the values calculated by the meter but this assumes there is not a standard that requires how values are calculated. 

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of