Metering and Monitoring systems

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Metering and Monitoring systems
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Johan_2023
Johan_2023
Cadet

Posted: ‎2023-11-27 10:13 AM

0 Likes
2
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-27 10:13 AM

Metering and Monitoring systems

Hi there,
I recently did a Schneider online course "Metering and monitoring systems for power reliability and availability".  In this course, some core features were mentioned for the meters, and I have a question about one of these features.

Power Meters (Incoming) : Individual Harmonics up to 511th 

Power Meters (Critical Loads) : Individual Harmonics up to 127th 

Power Meters (Feeder) : Individual Harmonics up to 31th 

I would like to know the technical reason for these 511, 127 and 31 th. Is there any technical reason why the incoming need to measure up to 511 th (and not up to 127 instead)? and same for Critical loads 127th and feeder 31?

What happens if the incoming can't detect up to 511?

 

My question is because when I specify these features in the EMS technical specification, normally the client ask me "Why 511th, why 127 and why 31". 

 

Why not only 127 for the incoming if after the 100th the effects are not considerable?


Thanks



Attachments
Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2023-11-30 03:42 PM

1 Like
0
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-30 03:42 PM

technically, meters will often have other limits besides just the Nyquist limitation for harmonic bandwidth.

https://en.wikipedia.org/wiki/Nyquist_frequency

 

For example if the device implements a low-pass filter (such as required by IEC 61000-4-30 Class A) then on some designs, although it may be mathematically capable of registering a result for the "255th harmonic" from a captured waveform, the reading may not be valid or useful (b/c the signal was attenuated below the noise floor)

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-11-29 09:16 AM

0 Likes
1
774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-29 09:16 AM

Hello @Johan_2023 ,

 

The maximum harmonic for a meter to be able to detect is (n/2 -1) where n is the sample rate. So a meter with sample rate of 1024 samples per cycle can have a maximum of 511th harmonic. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2023-11-30 03:42 PM

1 Like
0
760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-30 03:42 PM

technically, meters will often have other limits besides just the Nyquist limitation for harmonic bandwidth.

https://en.wikipedia.org/wiki/Nyquist_frequency

 

For example if the device implements a low-pass filter (such as required by IEC 61000-4-30 Class A) then on some designs, although it may be mathematically capable of registering a result for the "255th harmonic" from a captured waveform, the reading may not be valid or useful (b/c the signal was attenuated below the noise floor)

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of