Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Meter Selection

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Meter Selection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
sesa282957
sesa282957 Leader
Leader

Posted: ‎2015-09-18 01:53 AM

0 Likes
1
1168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-18 01:53 AM

Meter Selection

Dear Expert,

Please, i need a meter based on the below specification, kindly select the most appropriate meter.

 

The following are the minimum technical specifications for the programmable electronic grid energy meters for installation at the Nigerian Electricity Grid/Trading Points- 

 

 

POWER SUPPLY: 

 

Voltage: -     3x 11000/110V ,33000/110V, 132000/110 and 330000/110V.         

 

Current: -     3 X -/1A           3 X -/1A,      3 X-/5A

 

Frequency: – 50Hz

 

System: - 3-Phase 3 wire (or 3-Phase 4 wire for 11,) 33, 132 and 330KV

 

Secondary voltage variation:  85V—135V

 

Supply frequency variation           +5%

 

Internal Battery: -   Lithium CR20255 –1HF or an equivalent giving a total

 

                             Stand-by life of 10 years (minimum)

 

Auxiliary Battery: -            Embedded in the meter for down-loading  stored

 

data during power outage         

 

 

ACCURACY CLASS

 

  •   0.2   for 132, 330kv voltage levels and for loads above 50MVA.
  •   0.5   for 11 and 33kv voltage levels.
  • 1.0/2.0 LV, Ring CT Operated- for 415V LV voltage level
  • *MUST BE DLMS/COSEM COMPLIANT - For interoperability with other meter makes, with respect to AMR.

    ENVIRONMENTAL CONDITIONS

    Operating Temp Range:     -        -15oc to 60oc

    Storage Temp Range:        -        -15oc to +70oc

    Humidity: - Annual mean 75% (for 30 days spread over one year, 95%)

    BURDEN

    Voltage Circuit: -                                 1.12W or 2.45VA

    Current Circuit: -                                  /5A Meter 0.12 VA

                                                              /1A Meter 0.02VA

    CASING

    Material:-   The casing shall be for panel or wall mounting with fire retardant type of Bakelite or Polycarbonate.

    Screws: -      All Screws should be stainless steel or nickel – plated brass.

    Current Terminals:                               Screw type 2 per terminal (6mm)

                                                             Cable size: 4.0mm2.

    Voltage Terminals:                                Screw type: 1 per terminal (4mm)

                                                              Cable:  2.5mm2 .

    Auxiliary Terminal:                                Screw type: 3mm

                                                              Cable:  1.5mm2.

    INSULATION

  

  • 2.0 KV for 1 minute for current circuit
  • 2.0 KV for 1 minute for voltage circuit
  • 4.0 KV for 1 minute for current, voltage, all relay contacts plus auxiliary inputs plus the RS232/485 ports together.
  • 4.0 KV for 1 minute between all relay contacts and the auxiliary input plus communication port (RS232 or RS485)
  • 4.0 KV for 1 minute between one set of relay contacts and the other relay contacts.

    NAME PLATE

    The name plate should contain the following:-

  

  • Meter serial number
  • Operating current and voltage
  • Accuracy class
  • Frequency
  • Pulse nominal value etc.                                                                                                                                          

    Measured Quantities

  

  • Import KWH
  • Export KWH
  • Import KVArH
  • Export KVArH
  • Apparent KVA maximum Demand
  • Four Quadrant KVArH
  • Load Profile (180-450days)
  • Line parameters e.g. line voltage, current, power factor, active and reactive power, phase angle, frequency and phase rotation.

    TARIFFICATION:-                    Time of use register

                                          Maximum demand register

                                          Integration period options: 15 min, 30 minutes etc.

                                          Switching times

                                          Seasons times

                                          Billing dates

                                          End of billing dates etc.

    DISPLAY

    The display should be capable of displaying Default, Customer and Utility modes.

    - Battery backup operated display is required.

    EVENTS  MONITORING

    The meter should be able to monitor the following events among others:-

             

  

  • Battery fail indication
  • Battery elapse warning
  • Meter fail Indication
  • Reverse run warning
  • Over Current
  • Phase failure
  • Current reversal
  • Voltage reversal
  • Partial demand
  • Meter communication event
  • Time and date of events etc.

    DATA STORAGE

    It should be capable of storing measured quantities as end-month historical values for up to 16 months.

    COMMUNICATION

  

  • RS232 and RS485 must be fitted as standard
  • Optical port: - Opto – electronic, bi-directional
  • Protocol: -    Flag IEC 62056 - 21 (formerly IEC 61107)
  • Built-in GSM/GPRS Modem with omni-directional antenna
  • Must be compatible with MV 90 AMR Machine for end-month data retrieval.

    SAFETY CLASS

  

  • Category -    EN61010, EN61011 Class II

    REAL TIME CLOCK

  • Type: - Capable of synchronizing to A.C. Supply or to a crystal

                            Oscillator

  • Accuracy: -    Better than 0.5 of a second per day at 50oC

    ADDITIONAL INFORMATION

  

  1. The Energy Meters should be taken to a NERC certified Meter Test Laboratory for Type Test and Accuracy Checks, for a fee.

  2. Enough space should be made available on the Control Panel for Mounting of the meters.

  

 

  1. The Programming of the meters to the line CT, VT and display sequence should be carried out at the Meter Manufacturer’s Factory for accurate display of billing parameters.

 

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Anonymous user
Not applicable

Posted: ‎2015-09-23 02:17 AM . Last Modified: ‎2022-10-18 10:47 PM

0 Likes
0
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-23 02:17 AM

Hello sesa282957,

We have the global meter selector app to help you to select meter based on different conditions and applications

Please find more information below:

https://community.se.com/message/67809#67809

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore