Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84796members
354245posts

Looking for a meter compatible with Profibus

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

sesa297227_brid
Crewman Crewman
Crewman
0 Likes
4
852

Looking for a meter compatible with Profibus

Hi everyone,

I have a customer who has several ION7300 on a Profibus network and one is damaged and needs to be replaced.

Does anyone know if the PM8000 or any other meter is compatible with the Profibus protocol?  Or else, if there is any gateway available in the market that is capable to convert from Profibus to Modbus?

Thanks in advance!!

4 Replies 4
sesa186702
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Re: Looking for a meter compatible with Profibus

Hi Arturo,

As I know, just ION7300 series support Profbus protocol, new generation PM8000 just support Modbus, ION, DNP3, and IEC 61850

A recommendation for you is using Modbus RTU-Profibus DP Gateway: LUFP7- a product of SE

Here is a example for configuration PM710 with LUFP7

http://www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/35000/FA3520...

sesa297227_brid
Crewman Crewman
Crewman
0 Likes
0
781

Re: Looking for a meter compatible with Profibus

Thanks for your response Dang-Ming.

I will review if we offer this gateway in Mexico.  Hopefully yes.

Regards,

Daniel_Borle
Commander Commander
Commander

Re: Looking for a meter compatible with Profibus

Hi Arturo,

To work with LUFP7 for communicating had been introduced by us, about 10 years ago. The problem with this solution is, that this will be a "closed" system as you don't have any chance accessing the device then over Modbus. But about 1 year ago I found another solution:

We are using now a gateway which is called X-Gateway from the company HMS. It's the same company that also develops the LUFP7 (which is a labeled product). The advantage of X-Gateway is connected to Profibus DP over serial Sub-D9 connector as usual an one side. On the other side it is connected to Ethernet with Modbus-TCP. The advantages are as follows:

1. You can connect to different devices over Ethernet (e.g. EGX100/300 with connected devices, IFEs or devices with direct Ethernet connection like PM8000...)

2. The system is open for us, as we are communicating over Ethernet and not serial

3. The device can be configured over Web-Browser (no need for configuration software like LUFP7)

4. X-Gateway is also available with other protocols like e.g. Ethernet/IP

But be careful, as both solutions have some restrictions:

On one LUFP7 you can connect maximum devices and the total amount of registers that can be read from all of the connected devices is 122 (=> with 8 connected devices this makes around 15 registers per device). On the X-Gateway you have a maximum number of transactions of 64 (a transaction is a Modbus request) and the maximum number of registers is limited to 128.

Here you can find the link to the HMS homepage:

Anybus X-gateway - Connecting any two industrial networks or PLC systems

Best Regards

Daniel

sesa297227_brid
Crewman Crewman
Crewman
0 Likes
0
788

Re: Looking for a meter compatible with Profibus

Great answer!  Thanks!  I will look and quote this gateway.