Isuues with Acti9 Power Tag Alarms and Monitoring via DCE

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Isuues with Acti9 Power Tag Alarms and Monitoring via DCE
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
ThisIsJimmy
Crewman ThisIsJimmy
Crewman

Posted: ‎2022-07-25 05:30 AM

1 Like
1
750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-25 05:30 AM

Isuues with Acti9 Power Tag Alarms and Monitoring via DCE

Hi All

 

I am currently trying to setup the monitoring alerts from Power Tag, but I am encountering a few issues.  Some I believe are related to firmware on the Power Tag, and some are related to DDF files for the Acti9, but i'm not 100% sure on this and would appreciate some assisttance.

 

Smart Tag Acti9

 

Firstly, on the Acti9, I am seeing differences between Active Alarms (shown below)

 

Acttive AlarmsActtive Alarms

 

and the current Configured Alarms (below) which the above alarm does not feature nor is an option in the default list.

 

Default AlarmsDefault Alarms

 

I have updated the latest firmware via Power Comission (V2.1.5), but this still exists.

 

DCE

 

DCE is also generating Voltage and Current Alarms that are not being seen on the Power Tag across all slaves.  This is an example.  These are not on all the time, or appear for every slave at the same time, but keep being constantly generated

 

Current AlarmCurrent Alarm

 

Below are the only device specific Alarms that are generated.  These dont appear to match the configured device alarms.

 

DCE Device AlarmsDCE Device Alarms

 

I have tried running a Graph to see if their are any spikes or obvious conditions here that would cause this but from an example device I am seeing below it is not obvious to me where the issue is.

 

7 day report7 day report

 

 

I have downloaded the latest version of the Acti9 Power Tag DDFs that I can find (Version 2), but this has not changed anything.

 

Any help would be greatly appreciated.

 

Kind Regards,

Jimmy

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-08-18 04:37 AM

0 Likes
0
649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-18 04:37 AM

Hello Jimmy,

 

 

Concerning the 45% alarm in PowerTagLink web page: unfortunately the 45% alarm can not be disabled in the configuration. therefore this alarm is alway displayed as soon as the condition are fullfiled . refer to the previous post hereunder for detail 

 

https://community.se.com/t5/Metering-Power-Quality/PowerTag-Disable-Alarms/m-p/400111#M6293

 

Concerning the DCE alarms: I dont know your DCE system but I assume that the communication  is based on Modbus TCP/IP protocol . Therefore only the alarms bits listed in the Modbus register column of the table hereunder (extract from the PTL user guide) can be used to raise alarm.

Perhaps some aditional alarms based on PowerTag measure (current, associated breaker range...) are calculated and generated in the DDF file .

 

For my 2 cents!

 

PowerTag Link alarm synthesis.jpg   

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions

See Answer In Context

  • Thumbnail of PowerLogic™ PowerTag
    Schneider Electric
    PowerLogic™ PowerTag
View products (1)
Tags (1)
  • Tags:
  • english
Reply
Reply 1
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-08-18 04:37 AM

0 Likes
0
650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-18 04:37 AM

Hello Jimmy,

 

 

Concerning the 45% alarm in PowerTagLink web page: unfortunately the 45% alarm can not be disabled in the configuration. therefore this alarm is alway displayed as soon as the condition are fullfiled . refer to the previous post hereunder for detail 

 

https://community.se.com/t5/Metering-Power-Quality/PowerTag-Disable-Alarms/m-p/400111#M6293

 

Concerning the DCE alarms: I dont know your DCE system but I assume that the communication  is based on Modbus TCP/IP protocol . Therefore only the alarms bits listed in the Modbus register column of the table hereunder (extract from the PTL user guide) can be used to raise alarm.

Perhaps some aditional alarms based on PowerTag measure (current, associated breaker range...) are calculated and generated in the DDF file .

 

For my 2 cents!

 

PowerTag Link alarm synthesis.jpg   

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
  • Thumbnail of PowerLogic™ PowerTag
    Schneider Electric
    PowerLogic™ PowerTag
View products (1)
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of