Ion 9000 is showing double the amount of VARs compared to other metering in the substation.

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Ion 9000 is showing double the amount of VARs compared to other metering in the substation.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
502
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
103
Robert_Lee
Admiral Robert_Lee Admiral
93
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
sesa4025_bridge
Crewman sesa4025_bridge Crewman
Crewman

Posted: ‎2025-08-04 08:37 AM

0 Likes
1
37
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 08:37 AM

Ion 9000 is showing double the amount of VARs compared to other metering in the substation.

We have looked at the phasor diagram and can see what the meter is seeing.  Everything appears to be in phase.  The issue is that the Ion 9000 is showing double the amount of VARs compared to other metering in the substation.  I know this has been an issue before, I had found a thread online discussing this very issue where they had to add a “triangulation module” to change the way the meter calculated the data.  Are you familiar with that at all?  It appears we are experiencing that same problem, and I am assuming it has to do with the CT circuits being wired in a delta configuration.

 

 I have an ION 9000 power quality meter at my company’s Park Substation location. We have noticed that the meter is reading VARS and Watts incorrectly compared to our Bitronics meters. We think the magnitude of the voltage
and current being read by the meter is correct, as the total VA match the Bitronics. For example, right now it is reading Vll avg of 12, 646 V, an I average of 478 A, a Vln average of 7,305 V, 6,734 kW, 8,134 kVARs, and 10,341 kVA. Our Bitronics are currently
reading 9.9 MW, 3.7 MVARs, and an I average of 485 A (These were all instantaneous values that are bouncing around a bit as I read them). We think the problem may be that the CTs for the meter are wired in delta, and we have not found an option in the configuration
to specify this. Since the CTs are wired in delta to get the current magnitude of 478 A we set the CT’s primary value to 692.82 which is 1200 / √3. The PTs are in wye, and there is a setting in the configuration to specify this. It appears if we could offset
each phase’s current by +30 degrees it would fix our problem. Is there a way to do this? Or, is there another solution to our problem?

Attachments
Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-08-04 10:44 PM

0 Likes
0
20
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 10:44 PM

Hello @sesa4025_bridge 

 

Do you have a  wiring diagram of how the meter is connected to the system? 

 

I will start by saying I am a bit confused. The screenshot is from a meter that is not ION9000 based on the serial number. The values for voltage and current do not match your description.

When ION meters are showing kW that does not meet expectations when voltage and current magnitudes are at expected values, the most common issue is incorrect wiring. 

Also I am confused what you mean with changing the CT primary value. The setting on the meter should be matching the physical CT.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of