Hi All,
Do we have the IP rating for the HMI on the AccuSine enclosure? According to the catalog, I only found the IP rating for the enclosure, but the customer is especially inquiring about the IP rating for HMI. Thank you.
Best regards,
Link copied. Please paste this link to share this article on your social media post.
The AccuSine HMI (Magelis touch screen display) front panel which is mounted flush to the door (Outside part) is rated IP65. The internal portion of the display (Inside the enclosure door) is rated IP20.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
The AccuSine HMI (Magelis touch screen display) front panel which is mounted flush to the door (Outside part) is rated IP65. The internal portion of the display (Inside the enclosure door) is rated IP20.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.