is it possible to use non-standard ports for communications, i.e. instead of 502 can I use 504?
Thanks,
Dennis
Link copied. Please paste this link to share this article on your social media post.
Earlier versions of ION Setup would only communicate Modbus TCP on port 502 (all other ports would be treated identically to ION protocol and gateway operation). Recent versions of ION Setup will also use ports 501 and 503 similarly to 502 for Modbus TCP communications.