Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hi guys,
Does someone know whether it is possible to use SE Rogowski coils directly connected to ION9000s that have LVCS inputs or not?
Thanks
Daniel
Link copied. Please paste this link to share this article on your social media post.
Hello @Daniel_Borle ,
Directly connected, no. The output of Rogowski coil CTs are a derivative of the current. The meter does not process this kind of signal correctly. There are CTs or hardware out there that can process Rogowski coil outputs to something the ION9000 meter will expect. No I do not have a part number I can give you or even brands. I just know they exist.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Daniel_Borle ,
Directly connected, no. The output of Rogowski coil CTs are a derivative of the current. The meter does not process this kind of signal correctly. There are CTs or hardware out there that can process Rogowski coil outputs to something the ION9000 meter will expect. No I do not have a part number I can give you or even brands. I just know they exist.
Regards,
Charles