Hi guys,
Does someone know whether it is possible to use SE Rogowski coils directly connected to ION9000s that have LVCS inputs or not?
Thanks
Daniel
Link copied. Please paste this link to share this article on your social media post.
Hello @Daniel_Borle ,
Directly connected, no. The output of Rogowski coil CTs are a derivative of the current. The meter does not process this kind of signal correctly. There are CTs or hardware out there that can process Rogowski coil outputs to something the ION9000 meter will expect. No I do not have a part number I can give you or even brands. I just know they exist.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Daniel_Borle ,
Directly connected, no. The output of Rogowski coil CTs are a derivative of the current. The meter does not process this kind of signal correctly. There are CTs or hardware out there that can process Rogowski coil outputs to something the ION9000 meter will expect. No I do not have a part number I can give you or even brands. I just know they exist.
Regards,
Charles